Dear all... I have 1 0-400 duplex type RTD, I connected the
A side to the temperature indicator and B side to the PLC
panel, but when I have observed then found that The PLC side
temp has the variation. and it was distub to other RTD temp
also. so what can I do.
Answer / carl_ellis
The RTD element is ALWAYS isolated from the sheath. Dual
element RTDs should be isolated from each other.
Therefore, there should be no common electrical connection
between any wire in a dual element RTD.
The fact that a connection to one receiver (the PLC)
disturbs the other receiver's RTD reading means either
a) the RTD elements or lead wires are shorting to either
the sheath, the other RTD element or a lead wire; meaning
the RTD assembly is damaged internally.
b) the field wiring for one RTD is shorting to the field
wiring of the other RTD
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 0 No |
how to make temperature closed loop
how to connect 3 wire 4-20 mA transmitter in Plc system PLC system and how explain how the measuring data communicate with plc system.
pressure gauge measure static pressure or dynamic pressure?
can anyone guide me how to get any of the previous year GAIL question papers? are they available? 0n 2nd august i have to take the written test.
HELLO FRENDS ,, I M IN THE MIDST OF TROUBLE .. JUST LITTLE HELP ME... SUPPOSE ,, I HAVE A CLOSE VESSELE TANK ( HEXANE MEDIA ) ,, I M USING ROSEMOUNT 2051 DPT FOR LEVEL APPLICATION .. ITS CALIBRATE RANGE IS.. . 0 TO 950 MMH20 ..I DID CALIBRATED DPT WITHOUT REMOVING IMPULSE LINE OF HIGH AND LOW TAPPING.. & WITHOUT DISTURB 3 WAY MANIFOLD..!!! BUT ,,, DURING CALIBRATION I SELECT RANGE BY HART LRV IS 900 MMH20 & URV IS 1300 MMH20 ,, BUT ,TANK LEVEL SOMETIMES 100 % AT 1100 MMH20 , SOMETIMES 1300 MMH20 ..IN THIS CONDITION .. WHOLE LOOP FAILED ,, MAIN THING IS THAT ,, HOW TO CUSTOME RANGE SELECT ?? AND IF I USED RANGE OVER THE ORIGINAL CALIBRATE RANGE ,,,THEN WHAT ERROR WILL BE COME ??? HOW TO ZERO CALIBRATION OF DPT... HOW TO ZERO TRIM BY MANIFOLD ?? AND FOR TANK LEVEL PURPOSE ... WHICH UNIT I CAN USE ??? IS THERE ANY CALCULATION OR CALIBRATION .. IF YEH .. THEN PLZ JUST GIVE ME CALIBRATION STEPS FOR DPT.. THANKS YOURSSSSSSS
How much Resistance Show by RTD(PT100) when it is installed in process(Consider Process Fluid temp 29 Deg C)?
What is mean by analytical instrumentation?
what is dry leg and what is wet leg?
Name different parts of a pressure gauge. Explain the use of hair spring in the pressure gauge.
how to calculate range of level transmitter?
DC motor and DC Drives working funda?
calibration of instruments.