Dear all... I have 1 0-400 duplex type RTD, I connected the
A side to the temperature indicator and B side to the PLC
panel, but when I have observed then found that The PLC side
temp has the variation. and it was distub to other RTD temp
also. so what can I do.
Answer / carl_ellis
The RTD element is ALWAYS isolated from the sheath. Dual
element RTDs should be isolated from each other.
Therefore, there should be no common electrical connection
between any wire in a dual element RTD.
The fact that a connection to one receiver (the PLC)
disturbs the other receiver's RTD reading means either
a) the RTD elements or lead wires are shorting to either
the sheath, the other RTD element or a lead wire; meaning
the RTD assembly is damaged internally.
b) the field wiring for one RTD is shorting to the field
wiring of the other RTD
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 0 No |
if the neutral and ground of ups voltege are connected together in the source itslef then why the voltege b/w neutral and ground comes positive in some other destination inspite of having earth pit. how can we mimmise this?
what is Dry Leg calibration and where is it used
Which type of diaphragm use in costic line, dm water line, natural gas line, oil line?
How to Calibrate Coriolis Flow transmitter in field
Why using negative voltage in vibration measurement?
What is first echo & echo window in radar type level transmitter?
square root calculation for dp flow transmitter? give me a explanation with example
How RAL(Rotary air lock)works in cement industry?
Explain Three way boiler.
Which products are available in the Mass Systemswitch and System Manager AC range?
why 4-20 mA signal is preferred over a 0-10V signal
why we use impulse line of flow transmitter at 45 deg. angle both side of orifice plate.