If the capacitor bank is installed in switchyard say
132/22kv then on LT side say 22kv/0.433kv is it necessary to
install capacitor bank for maintaining power factor. if pf
is maintained on HT side then will that be maintained on LT
side as well.if not then how&why??????/ please
explain...........
Answers were Sorted based on User's Feedback
Answer / vijaykumarht
The capacitor bank on HT side will anyhow correct the PF,
the line losses will not be reduced. hence by putting the
capacitors on LT side, that too nearer to the load, the
losses and PF can be much better improved. The capacitors on
HT side is just to minimize the line losses, even though it
improves PF putting capacitors on LT side is always
recommended that too nearer to load, so as to get efficient
usage of electricity.
Please not that this answer is only for inductive load
consideration as linelosses and transformers and most of the
loads conneted to the line is inductive.
| Is This Answer Correct ? | 23 Yes | 1 No |
Answer / zahid noor
If capacitor bank is installed in switchyard & capacitors
are connected on HT side , it will try to balance losses of
transmission line and not towards LT side, where as for
maintaining /increasing LT side voltage, we need to install
seperate capacitors nearer to load so as to maintain PF at
LT side also depending upon connected load & distance of
equipment connected in LT side.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / kola raju
If the capacitors are installed in the ht side the pf of
the line improves but not the plant.And the plant pf is in
poor condition only which may leads to the losses on our
side and reactive load on the transformer may increase so
even if we have capacitors on ht side it is advaisable to
kept the capacitors on load side also.
| Is This Answer Correct ? | 9 Yes | 3 No |
What is the classification of hydro projects based on installed capacity?
what is the function of compressor?
when the rheostat kept in minimum to maximum position in motors what will happen?
WHat is the general checks required for Dry type transformers
What is the count of hvdc transmission lines in india?
Hi frnds :) plz tell me that i have 100 KVA 3 phase generator so by thumb rule 100*1.4 = 144 amps and generaly we can operate at 80% load...so it will 144*0.8 =112 amps.... so now i m confused about single phase load.....if we use that generator only for single phase the that 112 amps is total single phase load or i can give 112 amps at red 112 amps at yellow and 112 amps at blue.... i mean that total single phase load that 100 KVA generator will take is 112+112+112=336 amp ??
How many energy meters can be connected on a 15VA Voltage transformer. please send a calculation sheet.
explain with the help of loading capability curve,reactive power generation and absorption from synchronous generator?
in a refinery one motor is suddenly stoped. what will do how can i findout the problem explain step by step
How to calculate Grid rotor resistance(GRR) losses in slip ring induction motor?
how the inductor will work on dc supply?whether it will work or not?
WHAT IS THE FORMULA FOR CALCULATING CURRENT RATING(DIRECT IN GROUND OR AIR) OF ARMOURED(XLPE) CABLE OF 4C,16Sqmm?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)