in three phase with neutral connection, what will happen,if
the neutral is in open condition with single phase
distribution panel
Answers were Sorted based on User's Feedback
Answer / m krishna
Simply your circuit is open circuit. No voltage appears
across your load. If your neutral is connected to ground at
panel end, then it behaves as before.
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / santosh kawade
If neutral is in open condition with single phase load, all
phase voltages will became unbalance, if load is lighting
load or home appliances there is high chances of lighting
bulbs will fuse or home appliances will burn.
Santosh Kawade
9224 69 3116
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / pillay
It depends where the neutral is in
open condition.
when all three phases are loaded with
single phase load and the main neutral
is in open condition than the voltage
across the load will vary according to
the load and the voltage can be as high
as phase to phase voltage thus resulting
in damage to electrical equipments, but
if they are loaded symmetrical than the
phase currents are balanced internally
and the voltage across the phases are balanced.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jey
Whenever A neutral Gets open, The circuit Gets open and Voltage will be Unbalanced across the load
Is This Answer Correct ? | 0 Yes | 0 No |
How will change the frequency in distribution side?
how to reduce shorting current in a slipring induction motor
why does in transformer the v/f ratio constant?
How to measure current and voltage in an ELV circuit
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
What is restricted earth fault protection ?
I Have 100Ah battery with 650VA Inverter, i WANT TO TAKE a Solar panel to charge my battery, so please suggest me,what rating of solar panel(with solar charge controller) can buy for a load of 450w for 4 hours
Is it necessary to install Lighting Arrester on both side side (i.e HT and LT) of Transformer in a transmission substation? if yes Why on both side?
What are the condition for parallel operation of transformers?
how to prepare the technical test
in india are trains run by DC or AC? if DC , from where it receives negative potential? because pentograph receives singe potential only?
We have a 1275KVA existing Transformer in a power plant project. Customer want to get it test & confirm whether it is a Dyn1 Transformer or not. Pleae let me know how to test it.