in three phase with neutral connection, what will happen,if
the neutral is in open condition with single phase
distribution panel
Answers were Sorted based on User's Feedback
Answer / santosh kawade
If neutral is in open condition with single phase load, all
phase voltages will became unbalance, if load is lighting
load or home appliances there is high chances of lighting
bulbs will fuse or home appliances will burn.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / m krishna
Simply your circuit is open circuit. No voltage appears
across your load. If your neutral is connected to ground at
panel end, then it behaves as before.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / pillay
It depends where the neutral is in
open condition.
when all three phases are loaded with
single phase load and the main neutral
is in open condition than the voltage
across the load will vary according to
the load and the voltage can be as high
as phase to phase voltage thus resulting
in damage to electrical equipments, but
if they are loaded symmetrical than the
phase currents are balanced internally
and the voltage across the phases are balanced.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / jey
Whenever A neutral Gets open, The circuit Gets open and Voltage will be Unbalanced across the load
| Is This Answer Correct ? | 0 Yes | 0 No |
Explain the working principle of servomotor
20 Answers ABB, Bhel, FANUC, GE, Jindal Steel and Power, L&T, SIA, Steelco Gujarat Ltd,
what is the difference between Ith & Iu rating in MCCB. Particularly on SACE ABB Circuit Breaker?
Why the transformers are rated in KVA ? in new view
WHAT IS RMU AND WHAT IS ITS FUNCTION AND HOW TODISCONNECT
what is reactive power (MVAR) and how it is control? how it is generate in powerplant?
What is the meaning of insulation leavel LI 75 AC 28 About scott transformer spcification
Why compensation is necessary in feedback control system?
What are the disadvantages if neutral current exists in grounded star transformer distribution system?
IF alternator SCR value will be high means what happen in alternator efficency at operating power factor of 0.8
What is the "IS" for Rising Main?
Convert a star connected network into a delta connected network.
we are operationing 3NOs 800 Kva generators by singronyus.specialey evening time our panel trip. the panel showing generator earth fault
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)