Answer / sam patel
i think that is not accurate calculator. which give you
data regarding cable .but from HP capacity u can easily
count amper capacity .
example : if you have 100 hp motor
so required current is 156.25 amper
so to find cuurent from hp , divide by it 0.64
so u can get amper capacity
from polycab , rr kabel ,finolex , havellas catalog
u can check current rating and find according cable size
so above 156.25 amp u require 3.5 core x 150 sq mm al arm
and 4 core x 95 sq mm cables are used
for more detail , u can contact me on my mail id
Is This Answer Correct ? | 0 Yes | 0 No |
Which modulation has higher data rates a.fm b.am c.qam d.qpsk
What is the formula to calculate the no load current of a single & three phase induction motor
How to calculate the volumetric capacity of a oxygen & Nitrogen gas Cylinder if pressure is 145 kg/cm2 & water capacity of cylinder is 67 liters.
how braking & making capacity of circuit breaker are calculated?
what is cogging and crawling
best manufacturer for busbar for outdoor switchyard having double bus bar scheme, can any one share technical specification of busbar. 132kv voltage ?
why is power supplied in 3 phase only? why not in 2 or 4 phases?
One Township having 850 house and each house load is 2.2KW single phase & 5HP 3 Phase motors of 10 Nos .Who can calculate 11 KV transformer capacity .dilip_bhasker@yahoo.co.in
What are the factors to be considered during the Synchronization?
how to calculate busbar size? ex:11000kva main what is the busbar size ?and how to select the correct one
how to calculate cooling requirement of datacentre from electrical load?
What is mean by making & breaking capacity of circuit breakers?