what are the problems are there
if power factor is leading
Answers were Sorted based on User's Feedback
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
Is This Answer Correct ? | 3 Yes | 1 No |
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
Is This Answer Correct ? | 2 Yes | 1 No |
When the power factor is leading, the capacitive kVAr is
more than the Inductive kVAr and this still has to be
supplied by the source. As kVA is the vector sum of kW and
kVAr, still for the given kW, you have to produce more kVA.
Alternately, for the given kVA, you can only convert
partially into useful work.
Secondary effects are voltage boost in the system,
availability of stored energy to feed the fault in case of a
fault, increase in the asymmetrical component of fault
current, increasing thus the peak value of the fault
current, etc.
Is This Answer Correct ? | 1 Yes | 0 No |
define digital electronic
if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?
What is the function of retrip in busbar?
As we use capacitor bank in 3ph ckt to improve PF, can we use capacitor in single ph domestric use, in house we have Fan,Mixer,electric cooker,iron,tube choke they also lag the system,because it is inductive load. if it is possible to improve PF of single ph system-- if yes- type of capacitor to be used,connection diagram, working in detail. if no-- list it.
AC is the magnitude of sinosudial-wave but we use cose value to determine power factor instead of sine value.
how many types of dc batteries standards are present?
what will happen if synchronous machine rotor fed from single phase ac supply
diff. between star, delta connection?
is KVAR (not reverse power) relay necessary to protect from excitor field failure on a brushless, synchroneus generator? Some people with previos experince tell me no but the manufacturers tell me it is designed for that purpose. Is it that it is only necessary for brushless generators and not the older style with the slip rings and brushes?
For testing 33kv cable hipot testing. How much kv we have to Apply .Give in details.
Why 268hp induction motor taking different current in three different phases? (In which two phase having same current and one having higher value compare to other 2 phases.)
what are different types of alternator and discuss about the methods of cooling
16 Answers Bhel, Jindal, L&T, Nalco, Vedanta,