L&T ACB C-POWER OF 800A FAULS TRIPING AT THE TIME OF 110KW
MOTOR STARTS WITH EARTH FAULT RELEASE
Answer / sudhakar g
HI,
First you have to check the settings of ACB breaker, If the
settings fault also it will be tripping. The following
settings you have to check in ACB are
1) Thermal Protection against " Overload faults ": Ir = 0.9
X 800A= 720A-Time delay = 2 sec
2) Magnetic Protection for " Short Circuit Faults " : Isd =
3 x 800A = 2400A- Time delay = 2 milli sec
3) Earth Fault Protection against direct fault between any
phase and the protection line : Ig = 200A (D)-Time delay = 2
milli sec
4) Instantaneous Protection against " Short Circuit Faults "
li = 3 x 3200 = 9600A for Big faults
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
Is This Answer Correct ? | 0 Yes | 0 No |
explain single phase series motor
What is the difference between a Vacuum Circuit Breaker and a Load Break Switch?
what is full wave bridge?
What is the use of insulation tester and how it is to be used.
Why starters are using the machines???
What is the function of wave trap in an electrical substation?
DIFFERANCE BETWEEN function of ELCB? function of rccb? function of mccb? function of acb? function of mcb?
How do we calculate tranmission line losses of a 132 KV tranmsission line. Please give some quick tips?
why voltage ratings of xmission are in 11, 33,66kv and why not 11.5 ,16,19 or any other
1 KW = how many kva
ELECtrical
2 Answers Bahwan Engineering, Bhel, Electrosteel, NBCC, Qatar Airlines,
is there any concept of armature reaction in Induction motor?