Answer / sudhakar g

HI,

First you have to check the settings of ACB breaker, If the
settings fault also it will be tripping. The following
settings you have to check in ACB are
1) Thermal Protection against " Overload faults ": Ir = 0.9
X 800A= 720A-Time delay = 2 sec
2) Magnetic Protection for " Short Circuit Faults " : Isd =
3 x 800A = 2400A- Time delay = 2 milli sec
3) Earth Fault Protection against direct fault between any
phase and the protection line : Ig = 200A (D)-Time delay = 2
milli sec
4) Instantaneous Protection against " Short Circuit Faults "
li = 3 x 3200 = 9600A for Big faults


I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

How can we calculate the efficiency of a Running (On-Load) Motor ? What parameters are required and what is the method ?

0 Answers  


what is differnt between metering CTs an protection CTs

10 Answers  


What is the acceptable resistance range of UPS battery

2 Answers   Cisco,


why we use Test Terminal Block in 11 KV and 33 KV electrical panels.

0 Answers   EMC,


IN 6.6KV 3 phase switch gear .i will give 6.6kv to R phase only to earth in during H.v testing (through H.v KIT).what happen remaining phases.how much voltage get remaining phases.why? explain.

1 Answers  






what is an S.C.R. and how do they work?

4 Answers   GE,


wHAT IS CAPACITANCE LATCHING? hOW TO CALCULATE CAPACITANCE LATCHING? hOW TO SOLVE THE PROBLEM IF CAPACITANCE LATCHING APPLIED?

0 Answers  


what is an invertor A.C.?

1 Answers   Ami Tech, Shubham,


What happens if we connect a single phase energy meter in reverse polarity.

0 Answers  


How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?

2 Answers  


WHAT IS MEANT BY INSULATION CLEARANCE IN VACCUM?

0 Answers  


Dear all, I want to use Induction motor to open and close a 1 ton door. How much power do I need. Thanks

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16637)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)