L&T ACB C-POWER OF 800A FAULS TRIPING AT THE TIME OF 110KW
MOTOR STARTS WITH EARTH FAULT RELEASE
Answer / sudhakar g
HI,
First you have to check the settings of ACB breaker, If the
settings fault also it will be tripping. The following
settings you have to check in ACB are
1) Thermal Protection against " Overload faults ": Ir = 0.9
X 800A= 720A-Time delay = 2 sec
2) Magnetic Protection for " Short Circuit Faults " : Isd =
3 x 800A = 2400A- Time delay = 2 milli sec
3) Earth Fault Protection against direct fault between any
phase and the protection line : Ig = 200A (D)-Time delay = 2
milli sec
4) Instantaneous Protection against " Short Circuit Faults "
li = 3 x 3200 = 9600A for Big faults
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
Is This Answer Correct ? | 0 Yes | 0 No |
How can we calculate the efficiency of a Running (On-Load) Motor ? What parameters are required and what is the method ?
what is differnt between metering CTs an protection CTs
What is the acceptable resistance range of UPS battery
why we use Test Terminal Block in 11 KV and 33 KV electrical panels.
IN 6.6KV 3 phase switch gear .i will give 6.6kv to R phase only to earth in during H.v testing (through H.v KIT).what happen remaining phases.how much voltage get remaining phases.why? explain.
what is an S.C.R. and how do they work?
wHAT IS CAPACITANCE LATCHING? hOW TO CALCULATE CAPACITANCE LATCHING? hOW TO SOLVE THE PROBLEM IF CAPACITANCE LATCHING APPLIED?
what is an invertor A.C.?
What happens if we connect a single phase energy meter in reverse polarity.
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
WHAT IS MEANT BY INSULATION CLEARANCE IN VACCUM?
Dear all, I want to use Induction motor to open and close a 1 ton door. How much power do I need. Thanks