L&T ACB C-POWER OF 800A FAULS TRIPING AT THE TIME OF 110KW
MOTOR STARTS WITH EARTH FAULT RELEASE
Answer / sudhakar g
HI,
First you have to check the settings of ACB breaker, If the
settings fault also it will be tripping. The following
settings you have to check in ACB are
1) Thermal Protection against " Overload faults ": Ir = 0.9
X 800A= 720A-Time delay = 2 sec
2) Magnetic Protection for " Short Circuit Faults " : Isd =
3 x 800A = 2400A- Time delay = 2 milli sec
3) Earth Fault Protection against direct fault between any
phase and the protection line : Ig = 200A (D)-Time delay = 2
milli sec
4) Instantaneous Protection against " Short Circuit Faults "
li = 3 x 3200 = 9600A for Big faults
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
| Is This Answer Correct ? | 0 Yes | 0 No |
what is cro
Will The Rated Capacity of 20 MVA ,220/6.6 KV, ONAN cooling Power Tranformer be increased up to 25 MVA with respect to its %Impedence by ONAF cooling with same rating..?
Can step down transformer works as step up one???
transformer 3 ph, 225 kva pri 480v, sec 208v. primary neutral connected to system, is secondary neutral to be grounded and how
Difference between copper earthing & aluminium earthing?
if we increase the frequency given to a transformer then wat will happen to the transformer size, whether it will increase?
We have one 500KVA transformer. We have tested REF relay and commissioned. After one and half year, due to some ground fault in one of the DB circuit Transformer tripped by REF relay. What will be cause and remedy. Please advise?
What is the effect of earth capacitance
when meggering a 3ph,480v oil reservoir heater on a regen gas compressor, why do I get a reading to ground when meggering phase to ground? shouldn't it read opened or is there something that makes it read closed? on the same heater, when ohming, it reads open. thanx
what is the slip of synchronous motor
why battery is connected in parallel ?
How much duration I can keep open the CT if it is under loading condition(100 Amp load)?
3 Answers Infosys, NTPC, Suzlon,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)