L&T ACB C-POWER OF 800A FAULS TRIPING AT THE TIME OF 110KW
MOTOR STARTS WITH EARTH FAULT RELEASE
Answer Posted / sudhakar g
HI,
First you have to check the settings of ACB breaker, If the
settings fault also it will be tripping. The following
settings you have to check in ACB are
1) Thermal Protection against " Overload faults ": Ir = 0.9
X 800A= 720A-Time delay = 2 sec
2) Magnetic Protection for " Short Circuit Faults " : Isd =
3 x 800A = 2400A- Time delay = 2 milli sec
3) Earth Fault Protection against direct fault between any
phase and the protection line : Ig = 200A (D)-Time delay = 2
milli sec
4) Instantaneous Protection against " Short Circuit Faults "
li = 3 x 3200 = 9600A for Big faults
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
xpression 'document.FrmQF.myemail' [
Which device of PlC does share load between DG sets when DG are running in perallel?
which VFD is better ( LT or HT)
What Should be the value of Vector Surge angle at Tripping and how to calculate it?
how many joints are allowed in underground HT cable of 1 KM
Write the current equation in series RLC circuits.
Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA
What are the basic components of the feedback control system?
Explain Random and Deterministic signals?
How to select batteries required for ups and the inverter if we Known load? And how AH is selected of battery?
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
hi friends ,iam working as genset AVR service engineer in electrical field from past 2 yrs throughout india . i plan to shift in some other job without travelling in same field because i con't travel,i dont know what i do for that so please guide me what job is suited for me,how i can serch the job please anybody helpme iam totally confused
A 100W electric lamp is supplied from a 115V, 60HZ source. The peak instantaneous power dissipated in the lamp filament is
WHAT ARE THE EFFECTS OF SERIES RESONANCE AND PARALLEL RESONANCE ON THE CIRCUITS PARAMETERS?
how to calculate the lightning arrester conductor @ no of earth pits required