Answer / guru
There are many ways for calculation of LUX and Illumination
level. I have given you the details for Point by Point
Method for calculating the LUX requirement
LUX = (CANDELA x COS(a) x F) / D^2
Where Candela = Luminous Intensity (cd/1000lumens)
COS(a) = Required Luminous Intensity at an Angle of
(a)
D = Mounting Distance of luminairy in meters
F = Maintenance Factor
This method is generally used for Outdoor Lighting purposes
| Is This Answer Correct ? | 9 Yes | 2 No |
what is the reason for using 110 volt and 60 hertz ac supply for using power distribution in America?
How can we findout the maximum efficiancy of Transformer? At which load?
draw single line diagram of UPS
1 Answers Adani Ports, Equate, IBM, SAP Labs, Socomec, TATA,
what is difference b/w bus duct & bus bar.
What is the acceptance value of leakage current in HI POT test
Can I Drain A Oil For Sample When The Transformer is Running? (Charged)
how does an energy meter works?
what type of motor is used in fan
Three phase power is measured with two wattmeeter for balance three phase load.the reading of one wattmeter is zero.we can conclude that the power factor of balance load is?
Difference between RCCB, RCBO and ELMCB.
capacitor is load free component but why ampare meter shows current when capacitor bank breaker close?
How to select the earthing transformer,for DELTA TO DELTA TRANSFORMER OR ALTERNATOR SIDE.Pls post your answers and calculation.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)