Answer / arvind
Yes it is possible,if two coils have same resistance but
supplied voltage is different as 75 v for 3 A and 150 v
supply for 6 a coil. from ohm's law.
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / man
even when applied voltage to both the coils are same we can
have different currents.as because the inductance of both
the coils can be different(since its single phase supply so
inductance will come into picture,which depends on the
dimension of the coils),so the impedance of the coils will
be different and hence currents will be different even for
same voltage.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / mohseen ahmed
according to ohms law V=IR......if voltage is contant then
there will b constant current following through
resistance..but if supply voltage is not constant then load
current may b different....i hope u got the answer...REGARDS
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / k.prakashchandra
The coil wound over an insulted iron former will draw less
current.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / noel c. tigas
Answer # 3 is incorrect. We need to analyse the statement.
Heating coils are surely resistive, hence, we can eliminate
inductance. Answer no.#1 is the correct answer. They
should have different power ratings; hence, their operating
voltage, also the formula P = Square of I x R.
| Is This Answer Correct ? | 0 Yes | 1 No |
why hv winding is not placed near to transformer core
Hi,Any one has idea regarding the KPTCL Recuirtments for AE'e & JE's for the year of 2009-10???Kindly help in regards..
difference between ceiling fan
24 Answers Altius Technologies, Raisoni, TCS, Uni Deritend,
how to calculate size of cable from motor current given and how to calculate full load current of a induction motor.
What is Long rod insulator and it's applications..? merits over the disc insulator ..?
For high voltage and low current Circuit Breaker preferred is vacuum circuit breaker.why?
What is the difference between KV,KVAR,KVA,KW?
6 Answers L&T, PowerHouse, YUI,
can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?
what is difference between neutral& grounding?
sourse is 66 KV / 350 MVA, transfarmer is 1000 KVA 6.6 / 0.415 kv, iF fault is 28.75 MVA on 0.415 KV Bus then calculat the Transfarmer Impidance
Why the wave trap is put in Y phse only in switchyard?why not in other phases?
What is a dc motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)