We have two 1 phase heating coils having same resistance
of 25ohm, but during operation one takes 3A and other 6A
Is it posiible Pls. explain
Answers were Sorted based on User's Feedback
Answer / arvind
Yes it is possible,if two coils have same resistance but
supplied voltage is different as 75 v for 3 A and 150 v
supply for 6 a coil. from ohm's law.
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / man
even when applied voltage to both the coils are same we can
have different currents.as because the inductance of both
the coils can be different(since its single phase supply so
inductance will come into picture,which depends on the
dimension of the coils),so the impedance of the coils will
be different and hence currents will be different even for
same voltage.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / mohseen ahmed
according to ohms law V=IR......if voltage is contant then
there will b constant current following through
resistance..but if supply voltage is not constant then load
current may b different....i hope u got the answer...REGARDS
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / k.prakashchandra
The coil wound over an insulted iron former will draw less
current.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / noel c. tigas
Answer # 3 is incorrect. We need to analyse the statement.
Heating coils are surely resistive, hence, we can eliminate
inductance. Answer no.#1 is the correct answer. They
should have different power ratings; hence, their operating
voltage, also the formula P = Square of I x R.
| Is This Answer Correct ? | 0 Yes | 1 No |
Input power is 380 - 450 V but with 45 - 55 Hz frequency - desired output is 415 V and 50hz with 1% variation permissible. CVT / Servo dont stabilize the Frequency - what is best solution??
what is the avr
6 Answers ArcelorMittal, Heidelberge Cement,
in cable joints procedure what electrical problems have been solved out ?
Can any answer me ,What will be the range of C.T coil for L&T energy meter EM301 used for 180 kva DG set
How transformer neutralshould earthed ? Transformer neutral connected to earth mat in substations, right or wrong ?
the winding of Gen and Motor is star or in delta ??? and why
What is the value of 3 phase voltage?
How to work meggar?
what is the std. earthing resistance for 440V system or m/c, 33000/440 Volt substation? What is the std.?
What is mean by hot and cold loop testing?
What is the comparison of PILC and XLPE cable
how to calculate the fault in substation
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)