Answer / arvind
Yes it is possible,if two coils have same resistance but
supplied voltage is different as 75 v for 3 A and 150 v
supply for 6 a coil. from ohm's law.
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / man
even when applied voltage to both the coils are same we can
have different currents.as because the inductance of both
the coils can be different(since its single phase supply so
inductance will come into picture,which depends on the
dimension of the coils),so the impedance of the coils will
be different and hence currents will be different even for
same voltage.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / mohseen ahmed
according to ohms law V=IR......if voltage is contant then
there will b constant current following through
resistance..but if supply voltage is not constant then load
current may b different....i hope u got the answer...REGARDS
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / k.prakashchandra
The coil wound over an insulted iron former will draw less
current.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / noel c. tigas
Answer # 3 is incorrect. We need to analyse the statement.
Heating coils are surely resistive, hence, we can eliminate
inductance. Answer no.#1 is the correct answer. They
should have different power ratings; hence, their operating
voltage, also the formula P = Square of I x R.
| Is This Answer Correct ? | 0 Yes | 1 No |
in elevator industries , how to calculate the required KVA for the elevator (elevator spec- 40A module , motor of 13.5KW, 20A)
1 Answers DLF, Tata Steel Limited,
If the Supply voltage is increased by n times, the cross section of conducter will [increase/decrease] by ________ times ?
What is mean by earthed & unearthed cable? Voltage grade of 1.9/3.3 kV(E), 3.3/3.3 kV(UE), 3.8/6.6 kV(E)what it indicates??
Why the standard of ambient teperature mentioned as 40 degree celcius in machines.
what is the reasons for blowing fuse
what is the difference between the following 2 situations ? 1)Line & Neutral=240V Line & Earth=230V Neutral & Earth=10V 2)Line & Neutral=230V Line & Earth=240V Neutral & Earth=10V
what is the difference between unarmoured & Flexible cable? How to identified?
0 Answers Priyanka Electricals,
Why we are use dol starter up to 10 hp
Can we perform parallel operation of two transformers when one transformer on load?
A 15 kw squirrel cage motor having a maximum efficiency of 90% on a continuous full load has temperature rise of 42 degrees celcius after 30 min and 52 degrees celcius after 1 hr under the above operation conditions. a) calculate its final steady state temperature rise on continuous load and the heating time constatnt. b) if the motor is operated on a short load for 9 min estimate its temperature rise. c) calculate the maximum overload that can be applied on a short, 9 min rating so that the temperature rise is the same as the final steady state temperature rise on continuous load.
How to decide cable tray size?
Sir,I have finished my B.E in the Stream of EEE.How Can I get C license for Electrical???Please Tell me the way...My mail ID is praba1003105@gmail.com Cell:7402474123
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)