which relay is better , instantaneous or IDMT relay .
Answers were Sorted based on User's Feedback
Answer / karthik
for metering, protection all will be taken in one CT --only core will be varied in that CT
for measurement -1s1,1s2
for protection - 2s1,2s2
only one CT is used
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / biswaindu parida
In a substaion we use different ratio of CTs for different purposes. Such as 200/1 for metering 400/1 for another back up, 800/1 for protection like wise. So suppose if a fault comes say around of 1200A then the secoundary level current for different Cts will not be same.
Lets analyse them indivisually.
1) The 800/1 Ct will read it as 1.5A. For that we can simply use Over current relay and trip the breaker.
2) The 400/1 Ct will read it as 3A . here we can use IDMT relay.
As per its function it will sends trip command to the breaker as soon as possible...because here the time of trip is inversely proportional to the amount of fault current
3) But however in case of 200/1 CT, it will read it as 6A. If it is a metering CT then it should be protected 1st. because it has less saturation point as compared to protection or back up CT. So here we will use instantaneous relay so that it will trip suddenly when the fault current goes above some pre defined value.
| Is This Answer Correct ? | 0 Yes | 3 No |
Difference between KW & kVA
If i am running of spindle at 2000rpm ,but How to spindle stop at the second I am resetting the machine in CNC machines
how to calculate the transformer losses.
Why does the phase voltage of two healthy phases become equal to the line voltage in case of an ungrounded neutral 3 phase star connected sytem when a single line to ground fault occurs ?
Draw the circuit of clapp oscillator?
What is the purpose of starter and choke in tube light?
9 Answers Chimay Brewery, TATA, TSPL,
why we use the 100% and 95% stator earth fault protection for the synchronus generator ?
0 Answers Operational Energy Group,
As per BIS, Earth pit resistence value?
what will happen power cables laid without gap in underground
How to select, design,size & calculate for 11 KV/33KV/66KV/132KV/220 KV/440 KV circuit breaker for HT side of transformer protection/HT distribution protection?
what is the difference between LLL and LLLG fault ?
For 415v,3phase,22kw rating of motor how to calculate MCCB rating
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)