Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

which relay is better , instantaneous or IDMT relay .

Answer Posted / biswaindu parida

In a substaion we use different ratio of CTs for different purposes. Such as 200/1 for metering 400/1 for another back up, 800/1 for protection like wise. So suppose if a fault comes say around of 1200A then the secoundary level current for different Cts will not be same.
Lets analyse them indivisually.
1) The 800/1 Ct will read it as 1.5A. For that we can simply use Over current relay and trip the breaker.
2) The 400/1 Ct will read it as 3A . here we can use IDMT relay.
As per its function it will sends trip command to the breaker as soon as possible...because here the time of trip is inversely proportional to the amount of fault current
3) But however in case of 200/1 CT, it will read it as 6A. If it is a metering CT then it should be protected 1st. because it has less saturation point as compared to protection or back up CT. So here we will use instantaneous relay so that it will trip suddenly when the fault current goes above some pre defined value.

Is This Answer Correct ?    0 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what will happen reduce the transformer voltage from 415v to 406v, is it save the energy,? are this methodis good to reduce the energy.?

1519


a 230v transformer with step down ratio 19:1.it has 2000turns on primary and rated 25va calculate max primary current no of secondary turns volts/turn

1538


what is your aim

1908


what is the principle of operation of tungstun bulb ??

1822


What is the Basic Difference bitween Long Shunt Connection and Short Shunt Connection in DC Generator?

2339


how hydrogen cooled alternator undergo maintanence ? that is hydrogen when come in contact with air can result into explosions .

1913


In Designing the rating & accessories of a MCCB how to choose the type of releases..means what is the basis for selecting, thermal magnetic, electromagnetic & microprocessr based releases

2021


why the making current is more than then the breaking current and if its true then its about a controling circuit or breaker power contact points

2065


what is the purpose of slope in the differential relay?why we are using two slope?but in busbar differential we are using only one slope.why?

2906


explain PV modules in solar energy generation.

1921


explain safety measures in alternator?

1776


Compare jfet’s and mosfet’s.

1276


i want to run 11kv star connected motor in 6.6kv with delta connected throught inverter, is it possible?

2030


What is the role of Dedicated earthing in UPS System?

3098


What is quadrantal symmetry?

1644