As per BIS, Earth pit resistence value?
Answers were Sorted based on User's Feedback
Answer / ramdarkmaster
Earth's resistance will differ from place to place....
it all depend's on soil resistivity... some places it may be red soil, were as in some places it may black cotton soil..
so we need to measure the resistance using earth tester..
but normally it will in few ohms.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / mukesh kumar
Copper earthing should be below 1 and GI Earthing below 3.
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / rajesh pal
Value of earthing G.I should be minimun <3 ohm this value we can use for body earth any machine D.G ,Transformer any other
and copper earth value shoul be < 1 ohm it will bettor for Nutruel earth for D.G and transformer and also connect with isolation transformer and some medical machines MRI, CT scan,kottery machine OT and other machine which require.
| Is This Answer Correct ? | 1 Yes | 0 No |
why CFL lamp requires less electricity than a normal lamp?/
Hello friends i am facing one problem in lighting panel. Frequently neutral link near to MCCB is burning(firing. What may be the reason for this one. Please answer me.
why DG rating in kva
for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?
which are the criterias needed to select the kind of neutral earthing(solid earthing,resistance earthing,etc.) at various voltage levels in electrical distribution?
How to select HT/MV cable size ?
how starting current in motor is reduced in case of motor in star connection.
why we use the 100% and 95% stator earth fault protection for the synchronus generator ?
0 Answers Operational Energy Group,
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor frequency at maximum torque point is A 3.33% B 4.44% C 5.55% D 6.66%
11kV capacitor bank of rating 2.4KVAR, is charged with protective relays of only over current & Earth fault &.......without Over Voltage, Under Voltage & Neutral Displacement Relay. Is it advisable??
Why a transformer is rated in kVA and not in kW??
What is the suitable transmission voltage?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)