For 415v,3phase,22kw rating of motor how to calculate MCCB rating
Answers were Sorted based on User's Feedback
Answer / ucmed_king
Refer Manufacturer coordination chart for required rating and model of MCCB.
There is a thumb-rule though. Convert KW to HP (KW/0.75), multiply it by 1.5 gives you the rated current. Multiply it by 1.5 for breaker value.
Here's the coordinartion chart:-
http://powertips-elec.blogspot.in/2010/11/selection-charts-for-dol-starters-l.html
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / akash
39Amp Per Phase is the actual load, but you can be on safer using side using 50/63Amp MCCB.
Is This Answer Correct ? | 6 Yes | 0 No |
if we increase frequency of line, then how will string efficiency varies with it.
in a delta-star with neutral grounding on star side what will happen if one star limb got opened at star point
WHAT HAPPEN IF LT SUPPLY 415 V FED TO THE HT 3.3KV MOTOR
What is the difference b/w RMU & substation
What is transient Phenomenon?
why do we need the body earth?
how to can we synchronize different capacity of DG sets.60kva& 250kva?
why surge suppressor in vaccum circuit breaker and it is only in motor feeder why not in tranformer feeder?no surge suppresor in ocb in motor feeder?
why voltage drop if we have connected 230 v ac suplly through diode to bulbe we found haft ie 110 voltage drop why it is
What is working principle of ACB and VCB?
How many types of instrument cables are there?
How to Prepare preventive maintenance shedule of machine tool.