Answer / swayanjit
kw IS THE ACTIVE POWER. IT IS THE POWER THAT CONSUMED BY THE
LOAD BUT KVA IS THE APPARENT POWER.
KVA=(KW/POWER FACTOR)
| Is This Answer Correct ? | 21 Yes | 0 No |
Answer / shahulsnfa
KVA is apparent power which can be treated as available
power. and KW is real power which means the power consumed
from the available power (apparent power)
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / gulmohammedibrahim
KW is real power which is consumed by machine to give output
Kvar is the reactive power ,this is the power used by electrical machines to set up and maintain magnetic flux on it
now KVA is the resultant power that is vector sum of real power and reactive power
kva=sqrtof(kw*kw)+(Kvar*Kvar)
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / arshadullah
KW means kilo watts its formula is (kw= kva*power factor)
kva means kilo volt amps (formula is (kva= kw/pf)
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pradyumna chandra panda
in other hand we can say that kw is the real power which is used by a load(*) and kva is the supply power required to meet that load(*).
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / vivek
KW is active power measurement and includes power factor in solving
KVA is reactive power measurement and does not include power factor in its solution
| Is This Answer Correct ? | 9 Yes | 11 No |
Answer / ronit
kw is unit for total power
kva is unit for real power
and unit for reactive power is kvar(VOLT AMPERE REACTIVE)
| Is This Answer Correct ? | 1 Yes | 3 No |
what is meant by power factor ?
the question is about buchloz relay why we called it buchloz relay
how does high earth to neutral voltage affect electronic equipment?
if receiving voltage is higher than sending ones what will be the effect of receiver
What are marginally stable systems?
what is meant by bus bar and outgoing/incoming breaker in an electrical/electronic circuit
can volts/Hz be relied upon to use 460v,60Hz electric motors on a 380v,50Hz power supply?
Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?
with out name plate details , how to find the metering ct and protection ct.?pls brif explaination about that.
condider as 100 w lamps glowing . for completing a one unit how much time it should glow
160 kw motor running use 2R* 150 SQ mm cable
how electricity is generated an supplied till consumer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)