how many testing use in power transformer?tell equipment
names?
Answers were Sorted based on User's Feedback
Answer / pradeep
There are so many testing are available to test a power transformer.
1. Turns ration testing : to ensure the no.of turns on each winding.
2. Winding resistance testing: To measure the resistance of each winding.
3. Vector group testing : To identify transformer vector group, which is very important for parallel operation.
4. Insulation resistance testing : To ensure the healthiness of transformer insulation resistance.
5. Impedance voltage testing : Important for parallel operation and loading condition assessment.
6. No load/ Short circuit testing : For the measurement of losses.
7. Partial discharge testing : To monitor the insulation imperfection/aging effect
8. Switching impulse/ lightning impulse testing : To measure the impulse withstand strength of the transformers.
9. Acoustic level measurement: To track the level of magnetic hum of the transformer.
10. Dissolved gas analysis: To identify dissolved gaseous in the transformer gases.
11. Dielectric testing : To measure break down potential of transformer oil.
And the count goes on...!!!
The type of testings carried out will vary based on the application and criticality
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sudhakar g
HI,
Power transformer is used in Switchyards where it can
supply the voltage from grid to grid and the strutcure of
the transformer is Delta to Delta connection. there is no
stepup or step down in that.
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
| Is This Answer Correct ? | 1 Yes | 2 No |
dear all, How do i increase UPS (1000VA)backup time ? i have connected 2 12v wold you please 120 aH battery externally. ups charge the lead acid battery only 12.7 volt. backup time only 10.00 minuts and gose off. can any one of you help me?
HOW TO SET THE EARTH FAULT SETTINGS IN ACB????????????
what is use of governer in diesle engine
WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.
How much of the total hydro power potential has been exploited so far in india?
How single phase & 3 phase motor select rotating direction ie clockwise/anticlockwise
hi , i have 150 kw loud and we need 50 m cabil,i want to know wich size cabil we use. thanks
What is the Maximum Power generation capacity of a Synchronus Machine ??
Explain Active power,reactive power,how its related to each other , & inductive ,capacitive.
why our power production in multiple of 11, in strictlly asking why our o/p voltage of alternators is 11kv only and whynot graterthan 15 and016KV?
what is diff between Ground/Earth & Neutral?
IN 6.6KV 3 phase switch gear .i will give 6.6kv to R phase only to earth in during H.v testing (through H.v KIT).what happen remaining phases.how much voltage get remaining phases.why? explain.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)