suppose generator rating is 50 kw,load is 25 kw,hw much d
generator ll generate?what about d remainin power?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
25 KW only.The governor controls the speed by regulating the
fuel feed.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / amit
it is a one generator & one load condition so whatever the load demands the generator will have to generate otherwise stability stats decreasing and finally it will stop.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the role of reactive powerin transmission and distribution?
why voltage drop will occurs in 3 phase line?
How to desaturate a saturated CT of PS Class?
How harmonic block test are conducted on relays ( Siemens,Areva ect )power transformer using omicron kit?
why transformer rating in KVA or MVA instead of KW n MW??
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
How vfd saving power.
Where we give genset o/p in home & industrial applications ?
what is the function of buchhos rely in transformer
is oil viscosity affect on motor current?
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
diffrence between abcb and mocb
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)