Answer / sudhakar g
First we have to calculate the load details
Ex: for 100 kw load
I=(kw*1000)/(p.f* 415v*1.732)
=173A
For cable manfacutrer they give the list of for these amp
how much cable we have to lay
If u want to calculate means u have to consider
1) derating factor
2) temprature coffiecent factor
3) kfactor
| Is This Answer Correct ? | 6 Yes | 1 No |
What is VCB? where it is installed at SP. What is SP?
what is the MF if CT ratio is 500/5 and in meter specification is 3.75 REVS/KWH? Thanks and Regards Selvendran.N
Pl. brief about break-down maintenance of machine tool.
What is the ideal power factor?
how can we change the rotating direction of single phase AC induction motors?
12 Answers Heubach Colour, L&T, MNM Jain Engineering College,
can we make a loop between neutral and body for grounding?
Difference between transition and diffusion capacitance
WHAT IS TANK CKT.?
how capacitor control the power factor/
How is the air circuit breaker quenching the arc. If it is by air means, where is it come from?
The Source internal resitanse Rs , When equal to Load resistance RL, the maximum transfered is of _____ % of input power?
What is 100% protection of generator? Why 95% protection is used not 100%?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)