how to determine the size of power cable according to load current
Answer / sudhakar g
First we have to calculate the load details
Ex: for 100 kw load
I=(kw*1000)/(p.f* 415v*1.732)
=173A
For cable manfacutrer they give the list of for these amp
how much cable we have to lay
If u want to calculate means u have to consider
1) derating factor
2) temprature coffiecent factor
3) kfactor
| Is This Answer Correct ? | 6 Yes | 1 No |
what is kvarh? Please define it With calculation General motors ?
what is the similarity and difference between ups and inverter?
Brief working principle of stabilizer,application & safety precautions
What is the difference between 11kv/110v & 33kv/110v ? If both 11 & 33KV give 110v then what is the diiference ?
what is apparent poewr, reactive power, & active power?
how we can calculate cable size of 230v,1 hp single phase motor ? panel to motor distance is 25 meter
According to IEC60034-14, When the vibration monitoring system required for motor Bearing. above which KW, it is required? and for what type of bearing the vibration probe is provided.
How can i modify the design of 3 phase induction motor to be as 3 phase synchronous motor??
Why do we perform an open-circuit test and short-circuit test on the transformer?
Why indicate only 440V to 3-phase supply.
pf of synchronius motor is unity, is it axact(=one) value. ?
How to select AC3 duty contactor for DOL & Star-Delta starters
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)