Answer / shan
one disc can withstand 11kv so that in 11kv we are using one insulator the same if 22 kv we use 2 disc and in 33 we use 3 disc if 132 kv we use 12 disc i.e(11kv * 12 = 132kv)
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / kinslevel
The Disc is made in
such a way that each
Disc can withold 11kv.
So, you can only use 2
of the Disc if perhaps
you want to increase
the transmitting
voltage to about 22kv
or more.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / chrisanand00
The above said all answers are correct. And the Disc designed to withstand 8KV and Impulse withstand voltage is 15KV. It is designed for phase to ground not for phase to phase.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mishra
the Disc designed to withstand 18KV so it can work without get puncher at 11Kv
the number of discs snnected by the formula
18*(KV * fluctuating voltage)
where fluctuating voltage is plus minus 6% according to IER in OH lines
| Is This Answer Correct ? | 1 Yes | 0 No |
We have a 62.5 KVA DG with Leyland engine and kirloskar slipring alternator. We have earthed the neutral, and another earthing for the dg body. is it necessary to isolate the dg foundation with rubber pads?
Can I use measuring current transformers in protection purposes?
Define active filter?
How to design the no. of ceiling fans required in 5mtr X 10 mtr X 3 Mtr hight room?
why AC signals are represented by sinusoidal waveform?WHY other waveforms not used for representation
what is resistance
hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"
When we need up only in o/p 440v, so why we use directly in 11kva in input?
0 Answers Lupin, Medhaj Techno Concept,
how do u calculate CT rating for 10 mva transformer
generator(Deutz 550kv)is runing for 2 hours with load of 900 amp and then it goes in shutdown with alarm fault messege of speed fault although heirtz reading fixed at 50,what does that mean
While connecting the flood light plug on to the 415 V distribution panel,there was spark and the cable got burnt. Three ignitors of the flood light also burnt of. The lamps are of 400 W (total 6 lamps) connected through 1.5 mm2 cable. The plug was immediately removed from the circuit. There was a 30 mA RCD connected and a 250 A MCCB; however both did not trip. What could be the possible reasons for the circuit devices not to trip?Can someone assist please. Additional info if needed can be provided.
How would you supply a single house hold load from a 3-phase supply coming out of a sub-station?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)