Answer / shariff
It can be step down from 66kV to 440V,but the problem is
above 33kV power transformers will be in treated as EHV,
and normally they will carry loads in terms 20 or 12.5MVA
etc. then for e.g for 20MVA the sec. current with 440V will
be 20x10E6/440=45kA( Normal rating), where this power
transformer cant be made practically with huge cuurent. So
practically we will go for 66kV to 11kV normally, where
Current is the limiting factor...
| Is This Answer Correct ? | 32 Yes | 4 No |
Answer / k.prakashchandra
Inside a factory it is feasible.But for public utility you
can not erect regular 66KV/433V substations say ,every 500
meters, as long LT distribution lines can not drawn in view
of current and voltage drop.
| Is This Answer Correct ? | 11 Yes | 3 No |
It increases the power transmission cost very high.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / jaheerabbas
if we are converting the 33Kv to 440v directly, wastage of
power is more in the form of heat,so that we required large
no of heat sink too....heat sink cost will be more compare
to transformer, so that we go for the step by step convertion
| Is This Answer Correct ? | 14 Yes | 10 No |
Answer / lakesh thakur
when we convert 66kv to 440v directly then transformer size
will increase & loses will also increase. So we should
increase the size of heat sinke. So directly we can say the
cost of whole our project will increase & also increase MVA
rating
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ved prakash
Basic insulation level at HV & LV side is also a big factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ramki
fulls , there is mutual coupling in between the windings , so for 66/33/11/133..like this we can found the mutual coupling as a nearly 1.......so wethis
| Is This Answer Correct ? | 2 Yes | 11 No |
Hi, My question is our total motor load is 55 kw.so what cable size required for main supply. Please reply
why we used servo motor insted of inducation motor?
what is the pperating squvance in transmission line for circuit braker, isolater & earthing switch.
What is the difference between ARC & SPARK?
how can we calculate that how much capacitor is needed for a system to increase the pf?
which of the following motors is non-self starting?
why a pilot exciter is used in combination with the main exciter? why not only a main exciter is used for excitation to an alternator?
In control room of our one plant there is a continuously the incoming power goes to PC is vary,means in stabilizer it continuously indicate from high input to low and low input to high. what is the reason and its solution.
why are transformers rated in KVA and not in KW
ELCP USE IN 3 PHASE SUBMERSIBLE PUMP? THEN USE 3 POLE 0R 4 POLE?
if we apply 1000ADC instead of 100ADC or We apply 50ADC instead of 100ADC,What will be happened in the test result value.Pl explain
What is OLTC AND RTCC and it's function?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)