Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why
not we convert directly from 66kv to440v?

Answers were Sorted based on User's Feedback



we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / shariff

It can be step down from 66kV to 440V,but the problem is
above 33kV power transformers will be in treated as EHV,
and normally they will carry loads in terms 20 or 12.5MVA
etc. then for e.g for 20MVA the sec. current with 440V will
be 20x10E6/440=45kA( Normal rating), where this power
transformer cant be made practically with huge cuurent. So
practically we will go for 66kV to 11kV normally, where
Current is the limiting factor...

Is This Answer Correct ?    32 Yes 4 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / k.prakashchandra

Inside a factory it is feasible.But for public utility you
can not erect regular 66KV/433V substations say ,every 500
meters, as long LT distribution lines can not drawn in view
of current and voltage drop.

Is This Answer Correct ?    11 Yes 3 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / yogender goel

It increases the power transmission cost very high.

Is This Answer Correct ?    8 Yes 2 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / jaheerabbas

if we are converting the 33Kv to 440v directly, wastage of
power is more in the form of heat,so that we required large
no of heat sink too....heat sink cost will be more compare
to transformer, so that we go for the step by step convertion

Is This Answer Correct ?    14 Yes 10 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / lakesh thakur

when we convert 66kv to 440v directly then transformer size
will increase & loses will also increase. So we should
increase the size of heat sinke. So directly we can say the
cost of whole our project will increase & also increase MVA
rating

Is This Answer Correct ?    3 Yes 0 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / ved prakash

Basic insulation level at HV & LV side is also a big factor.

Is This Answer Correct ?    1 Yes 0 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / ramki

fulls , there is mutual coupling in between the windings , so for 66/33/11/133..like this we can found the mutual coupling as a nearly 1.......so wethis

Is This Answer Correct ?    2 Yes 11 No

Post New Answer

More Electrical Engineering Interview Questions

What is mean by discrimination of circuit breaker ?

1 Answers  


can we step up dc power using transformer?

15 Answers  


Basic motor transformer generator

0 Answers   eCentric Solutions,


What are your future plans for the company if permanently employed?

0 Answers  


dg earth connect only in the amf panel or not why

0 Answers  


What is stub protection is all about?

1 Answers  


Why we are putting off the APFC(automatic power factor control) panel while the generator is running?

4 Answers   National Steel,


- two pumps must work with them at the same time but if the first pump start the second pump  must delayed for some time to start  also , with motor rated power = 90 KW and rated voltage = 380 V and rated power factor = 0.85 lag please draw the power and control circuit for it and determine all circuit components parameters that you use it

0 Answers  


Why you want to join non technical field when you are an engineer?

0 Answers  


how i can calculate the size for fire cable

0 Answers   Adani Power,


please I wont know how to calculate the vector group for power transformer ZNyn11 best regard.

0 Answers   Al Rasikh,


why it is not advisable to run low rating (19KVA) DG sets in parallel for long durations even though they are provided with droop ckts (QDC)

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)