Is 2000kva stabilizer suitable for 1h.p split air conditional
Answers were Sorted based on User's Feedback
Answer / jeetu ji
At 0.8 power factor, KW value of this stabilizer is 1600 KW
which is quite high value for 1 hp = 746 watt
We can use it but preferably a stabilizer of 1 KW is
sufficient.
| Is This Answer Correct ? | 7 Yes | 0 No |
Is there any scope for an electrical engineer in MRF company......
Why PS class CT is always preferred for Differential protection?
Why battery chargers are use in substation?
State the difference between Three winding transformers and Two winding transformers ? where its used?
(1)For 3 No 1500 KVA transformer require on one single bus bar or need to be section through bus coupler means upto 3MVA.(2) 22KV Net work system as ring, How maney I/C required or 0ne I/C and one O/G.(3) What should be rating of VCB for 22 KV line.(4)Electrical/mechanical inter lock, why we need.
in thermal power plants by opening the turbine governor valve increase the generator load. how
why all selected supply voltage are multiple of 11
why restricted earth fault protection can not operate for phase faults??as there will be a current in secondary of ct,when a phase fault occurs!
What may be happen if neutral and earth is shorted in a substation
WHAT ARE THE DATAS REQUIRED FOR SCS SIGNAL LIST PREPARATION?
Ho de we calculate the line loss of a 500 kv line over 1000km.
Which Programming software are use for Allen bradley PLC's?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)