Is 2000kva stabilizer suitable for 1h.p split air conditional
Answers were Sorted based on User's Feedback
Answer / jeetu ji
At 0.8 power factor, KW value of this stabilizer is 1600 KW
which is quite high value for 1 hp = 746 watt
We can use it but preferably a stabilizer of 1 KW is
sufficient.
| Is This Answer Correct ? | 7 Yes | 0 No |
Usage of flywheel diode in relays
If i have two 3000 kW motors and the whole facility requires a 10 MVA transformer. What would be better installing two 5 MVA transformers(one for 1 motor ) or just a single 10 MVA transformer for both of them. Give reasons for your answer.
why inductance is not present in a incandescnt lamp?
what is form factor?
What is the equipment used to control the generator output?
what is the difference between CT and CVT in EHV Sub Stations
4 Answers Hofincons, Lanco, TATA,
What must be the distance between the Earth pit which are grounded from two different sources. Example: Distance between the earth pit for LV Panel-1 & 2
what is the formula to calculate the fault level current for any substation?
After synchronizing the running generator with grid, the avr getting tripped and the generator breaker also oettong tripped, before tripping the avr the pf meter of generator is showing leading pf please kindly give a suggestion to rectify this problem.
what is the dis-advantage of 3 phase 3 wire energy meter?
How to Calculate IKW(input kilowatt)of a Chiller plant
What are the disadvantages of thermal power plant?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)