Is it possible to convert 4 wire transmitter to convert to
2 wire with additional relay.Please send detial with
drawing,i will appreciate.
Answers were Sorted based on User's Feedback
Answer / carl_ellis
No, it is not possible to convert a 4 wire device (power on
2 wires, output signal on 2 wires) to a 2 wire, loop
powered transmitter.
A 2 wire loop powered transmitter uses 3.7mA of the current
loop to runs its electronics. That's why the 'live zero'
starts at 4.0mA, so that there's some power avialable to
the transmitter's electronics.
There's lots of technologies that cannot run on the limited
power of approximately 3.7mA at 24Vdc. Thermal dispersion
flow meters, most wet cell gas detectors, thermal
ionization detectors, to name a few, which have to be 3 or
4 wire devices in order to have sufficient power to operate.
Carl Ellis
Measure First
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / amit
it's function ablavale in transmitter otherwise we do not
convert them.
Is This Answer Correct ? | 0 Yes | 5 No |
How do Foundation Fieldbus works? how the Communication Carries out from Foundation field bus,Field Devices and Controller? Were it's Application in the Field? For Which Signals this is Used? PLease Find this answer for this Question Detaile wise because i want to clear the Concept Regarding Foundation Field Bus,if Possible please attach the link of Document with Contails Diagramatic So that more esier for me.
Foe selecting control valve if i have the min,normal & max data of flow rate,inlet pressure& outlet pressure,inlet tem.&density than how can i assure that these data are correct,pl. let me know if therew there is any method to check it.& also how we assure that the Cv we get from this data is suitable for valve for controlling require flow.
i am confusing about differential pressure transmitter as i seen so many DPTs in different ranges how can we calculate level and flow with mmh20 plz tel me
What is the standard height for stancion supports?
HI, can anybody give details about GAS TREATMENT PLANT CONSTRUCTION,as INSTRUMENTATION ENGINEER what are the responsibilites.what are the instruments mainly instrumentation engineer will deal with
Calibration procedure for water rotameters
hi friends,im an instrumentation and contol engg student,can u hlp me of suggsting barc written question paper,my id is roysuvaranjan@gmail.com, cel no.9563591747
Which softwere is required to communicate the S7-300 processor
Identify and use the ANSI/ISA-S5.1 consensus industrial standard process symbols.
What is Positive Calibration and Negative Calibration?
Level in tank under vacuum (Ex: Condensate Tank of Power Plant)is measured using D. P. type level transmitter. Tank is subjected to vacuum of 755mmHg. Is it possible to fill wet leg ( i.e. leg connected to top of vessel with low point of D. P. xmtr) with water?. Are there chances of water getting sucked under vacuum? if yes, what is the solution?
Hi buddies! my name is sachin and i am working as a electrical and instrumentation engineer in a paper plant. right now i am facing a problem and if someone could help me it will be an immense pleasure to me. i am using AC 800M to synchronise DCS500 drives on paper machine and rewinder.communication is on PROFIBUS and we are using NPBA-01 module to link profibus to DC drives.But these days two of these drives are showing a error named FIELDBUS COMM.TIMED OUT and the drives get tripped.I have changed the NPBA module and PROFIBUS cable.So if anyone can do please help me out with this problem.I'll be highly grateful.