I have running 4 generator in paralel.All generators
Voltages is same(470 V),KW also same (100 KW) but only No2
generator Amper is high than another generators.
DG No:1,3,4 470V,100KW, 150 A
DG No:2 470V,100KW,400 A
Answers were Sorted based on User's Feedback
Answer / ruslan
Yes My friend it is possible.All meters are in good
condition.I also surprised.
Is This Answer Correct ? | 3 Yes | 0 No |
This is caused by kvar. If the excitation is higher (field
voltage) it will take more kvar. This will only be shown by
a current not load. The KW will remain the same.
Reduce the excitation (voltage setting on the AVR) on No 2
generator until it is reading the same current as the other
3 generators.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / afzaal
what?how could that be possible?with the same power ,the same voltage u get more amps....please check your instruments first..there must be some faulty meters..if not then i am too interested in knowing the answer of it
Is This Answer Correct ? | 1 Yes | 3 No |
why humming sound occured in HT transmission lines.
why current transformer secondary side should be shorted ?
static chagre
how does oil cools the transformer
Why derating factor os applied on Cables?
WHICH IS BETTER( FOR POWER SAVING)- ON LINE OR OFF LINE UPS ?
3 Answers Punjab National Bank,
what do u mean by bus bar?
Why LT cables are not sized based on short circuit capacity.
the circuit having same properties in either direction is known as.......
RESPECCTED SIR/MADAM- I AM PRERING FOR SECTION ENGINEER (ELECTRICAL) RRB CHANDIGARH PLEASE SEND ME SOME PREVIOUS YEAR QUESTION PAPER OR MODEL PAPER.MY EXAM IS ON (30- NOVEMBER 2008).I AM VERY THANKFUL TO YOU. FROM- HARENDRA SINGH YADAV
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side?