I have running 4 generator in paralel.All generators
Voltages is same(470 V),KW also same (100 KW) but only No2
generator Amper is high than another generators.
DG No:1,3,4 470V,100KW, 150 A
DG No:2 470V,100KW,400 A
Answers were Sorted based on User's Feedback
Answer / ruslan
Yes My friend it is possible.All meters are in good
condition.I also surprised.
| Is This Answer Correct ? | 3 Yes | 0 No |
This is caused by kvar. If the excitation is higher (field
voltage) it will take more kvar. This will only be shown by
a current not load. The KW will remain the same.
Reduce the excitation (voltage setting on the AVR) on No 2
generator until it is reading the same current as the other
3 generators.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / afzaal
what?how could that be possible?with the same power ,the same voltage u get more amps....please check your instruments first..there must be some faulty meters..if not then i am too interested in knowing the answer of it
| Is This Answer Correct ? | 1 Yes | 3 No |
What happened when a three phase induction motor work on two phase supply.9
when transformer in load condition neutral earth testing wheater we can do it or not
Who is reputed manufacturer of TNC switch for ACB in India ?
What is use of starter and choke in tube light
please forward me the type of questions which would rise while me attending to 33KV Electrical License to my mail ID:vadrevu_raghava@yahoo.co.in
i want to know that how the height of Ct ,cvt ,LA calculated on the basis of creepage distance
whati s the sludge current in ups
how i calculate the syncrones generator NGR resistance .if we have a 6mw generator line voltage of generator 11kv also line current 393.3 ampere.
what is the function and use of oil filled cables specify its advantages and disadvantages
What is the difference between reciprocating & rotary motors in AC units, which is the best one in terms of operation.
I have 2 transformers in two different plants, both are without OLTC but i am facing problem of voltage fluctuation at LV side from only one transformer. i have to change its taps manually twice in a day. Another transformer delivering voltage is ok. Please guide me about the problem
what is corona ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)