definition of fault level in powersystems?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The product of normal system voltage and short circuit
current at the point of fault is fault level and is equal to
3 Vph(normal) x Isc for symmetrical fault in 3 phase
system.It is expressed in KVA or MVA
Is This Answer Correct ? | 15 Yes | 3 No |
Answer / amit khamesra
Short circuit levelof the system defines its mechanical
strength to bear the enormour fources and heat developed by
short circuit current. To revamp a systm from 40 KA to 50
KA capacity, more no. of insulator suppors are required
along with increase in busbar current carrying capacity.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / isaac p
Fault level is a point where the normal operation level
has been exceeded and the system shuts down or other
components are called to rescue the situation.
Is This Answer Correct ? | 5 Yes | 7 No |
Answer / tarak mehta
It is the value which is exceed the normal value from where
the system can not ragain its healthy condition.
Is This Answer Correct ? | 5 Yes | 9 No |
in conclusion why we select you?
which type of breaker sould be used for different level of voltage ? (i.e at 11 Kv, 33 Kv, 66 Kv....
Trafo ratio is 11kV/6.6kv,Vector group is YND11. What will be the effect if secondary is used for earthed system.
Hi,, Just I want ask, if the power factor decrease what happen in voltage regulation? Thanks..
Phase control and integral control are used for?
what is high tension ? specify the range?
when giving a supply to wounded coil it will get magnetised, but the same is not if it is not wounded on a core..and it is getiing short....why.......
Dear All kindly let me know that I know about the DG Rating for Example 150 KVA,Now how i will know that how much Ampher load it can offoard.
Can we provide 3phase wire in conduit for room?
why star connected transformers used in tneb?
transformer phasor diagram under load explain it?
What is the diffrence between an ELCB(earth leakage circuit breaker) and RCCB(residual current circuit breaker)?which has higher degree of safety and why?