definition of fault level in powersystems?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The product of normal system voltage and short circuit
current at the point of fault is fault level and is equal to
3 Vph(normal) x Isc for symmetrical fault in 3 phase
system.It is expressed in KVA or MVA
| Is This Answer Correct ? | 15 Yes | 3 No |
Answer / amit khamesra
Short circuit levelof the system defines its mechanical
strength to bear the enormour fources and heat developed by
short circuit current. To revamp a systm from 40 KA to 50
KA capacity, more no. of insulator suppors are required
along with increase in busbar current carrying capacity.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / isaac p
Fault level is a point where the normal operation level
has been exceeded and the system shuts down or other
components are called to rescue the situation.
| Is This Answer Correct ? | 5 Yes | 7 No |
Answer / tarak mehta
It is the value which is exceed the normal value from where
the system can not ragain its healthy condition.
| Is This Answer Correct ? | 5 Yes | 9 No |
why wound rotor is star-connected?
Active power= VI COS FI But incase of leading power factor ( more than unity), may we use other formula ? because the cos fi (value of cos thita) should not be grater than one.
how to connect the three phase capacitor in three phase star/delta connection motor?
How much current flow in no load condition of a motor?
Factory acceptance test. FAT. For 132 kv transmisstion towers what is that meaning and what are the tests commonly companies perform now days.
hii this is ranjith from hyd... i want to know what type of questions they ask in interview...and hw the interview will go..? what subjects thay ask specially for electrical engg students?
How to calculate ht side cable of 630 kva oil cooled outdoor transformer?
What is surger vector in 33Kv transmission feeder? We have AC power generator of 8MW which is paralleled with 33Kv EB grid. Some times our HT breaker gets trip off due to surge vector problem. How to over come it? Is there any device to observe the surge and avoid tripping?
in electrical fire which group fier Extinguisher as used
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
HOW WE KNOW IN PHYSICALLY THE CONTACT SURFACE OF A VACUUM INTERRUPTER IS GOOD OR GOING TO DAMAGE IN A VCB AFTER ABOVE 500 TIMES OPERATED.
how speed control of induction motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)