Answer / manikandan
in 3ph 415 vac 4wire system the neutral used for 1ph electrical equipment power supply. i.e. nominal voltage 230V 1 ph can be obtained between any one phase and the neutral.
| Is This Answer Correct ? | 1 Yes | 0 No |
As to the domestic loads i.e lightning loads required the
neutral bcz of This High voltage supply its being connected
with the distribution substations here this voltage is being
step down low voltage by using transformer. Normally the
power transformer primary is formed in delta connection to
avoid the leakage currents and its secondary is formed in
star connection. as required above with the same.
Neutral & Earthing are tied together. neutral its carrying
charging current also acts as return path
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / wafiiq
We use 3PH 4 Wire system for secondary side (LV) side of
distribution transformers. The first 3 wires are the three
phases while the 4th wire is the neutral. Grounding the
neutral, a process known as system earthing, will allow
single phase users to have single phase supply from the
distribution transformer, i.e. nominal voltage 230V can be
obtained between any one phase and the neutral. Thus, by
grounding the neutral, we are making sure that it remains
at 0V, i.e. at the earth potential. As for 400V, is simply
the line voltage, between any two phases.
| Is This Answer Correct ? | 1 Yes | 2 No |
what is high - pot test. what's its use?????
why do you want leave the company
State four advantages of hydro power station over nuclear power station.
what is alluminium arm in ab conductors
What is control system?
Moving Iron instruments are applicable with a) DC only b) AC only c) DC & AC
14 Answers Bhel, Engineers India, Engineers India Limited,
what is the highest transmission voltage in India till now?
why we oltc on hv side of tranformer only
what is circuit recombiner and how it is different from circuit breaker
Explain the operation carried out in thermal power stations?
We have a distribution transformer of 750KVA/11kv/440v and an AVR (Servo Stabilizer) of 750KVA on the LT side of distribution transformer. Also we have an ACB of 1200A on the output of distribution transformer (that is on the input of AVR). We want to have an MCCB on the output of AVR. What should be the rating?
what is the difference between OSR and BUCHHOLZ relay of transformer?
1 Answers Bhushan Power Steel,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)