Answer / manikandan
in 3ph 415 vac 4wire system the neutral used for 1ph electrical equipment power supply. i.e. nominal voltage 230V 1 ph can be obtained between any one phase and the neutral.
| Is This Answer Correct ? | 1 Yes | 0 No |
As to the domestic loads i.e lightning loads required the
neutral bcz of This High voltage supply its being connected
with the distribution substations here this voltage is being
step down low voltage by using transformer. Normally the
power transformer primary is formed in delta connection to
avoid the leakage currents and its secondary is formed in
star connection. as required above with the same.
Neutral & Earthing are tied together. neutral its carrying
charging current also acts as return path
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / wafiiq
We use 3PH 4 Wire system for secondary side (LV) side of
distribution transformers. The first 3 wires are the three
phases while the 4th wire is the neutral. Grounding the
neutral, a process known as system earthing, will allow
single phase users to have single phase supply from the
distribution transformer, i.e. nominal voltage 230V can be
obtained between any one phase and the neutral. Thus, by
grounding the neutral, we are making sure that it remains
at 0V, i.e. at the earth potential. As for 400V, is simply
the line voltage, between any two phases.
| Is This Answer Correct ? | 1 Yes | 2 No |
WHAT CAUSED THRESHOLD VOLTAGE TO EXIST?
what is meant by reactive power ?
why generation voltages are 6.6kv or 11kv and why not some one give that stander that generation voltages are 5kv or 12kv?
What happened when a three phase induction motor work on two phase supply.9
What is earth system using on the floater TN-S or TT. Iam not sure and what ICCP
how to calculate busbar capacity for 1000Kva transformer having22/.433V
2 Answers Electrical Tech, L&T,
how instantanious short circuit current is calculated ? its formula.
why in an industry; machine having rated 200 h.p stopped after power factor is maintained above 0.97 lag by control panel in view-of energy saving
What is difference between insulating medium and fault current interruption medium in a switching device.
Which motor will you choose which can operate in both lagging as well as leading power factors?
without name plate detail of blower how we can find out the HP & Rpm ? the input voltage is 230v single phase
what do you mean by linear and bilateral network?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)