Answer / zahid ali
Vk is knee point of CT it mean when 10% increase in voltage
varies the current 50% at that point we determine the knee
point voltage. In othe words excitation test of CTs,
connect a single phase variable power supply leads to the
CT seccondary leads k & l or s1, s2 along with ampere meter
& voltage meter & than apply voltage start from zero &
raise incremental simultaneously draw a graph on each
increments by plotting current on X-axis & voltage on Y-
axis.
Magnetizing current is those which is used in core & tank
of transformer due to leakage flux, which is furthur
devided into hysteris losses & eddy current losses.
We can find magnetizing current by open circuit test.
5P10 means: 5 for composite errors in percentage, P for
protection & 10 mean overlaod factor by multiply 10 times
in others words CT will not saturate by passing 10 times
higher current.
| Is This Answer Correct ? | 84 Yes | 9 No |
Answer / v .selvakumar
knee point means at which the core tends towards
saturation .magnetising current means to produce flux in
the core it will take some current it is called magnetising
current.before knee point the graph between Vk and Imag
will be linear,at which point linear curve getting
disturbed .
| Is This Answer Correct ? | 31 Yes | 9 No |
Answer / ugrasen
Dear friend,
Knee Point voltage is nothing but a point at which the CT
saturates. Thatsy its always better to design the CTs which
can operate without saturation even at a voltage appears in
the CT during fault condition. Pls find below the following
formula for calculating the Knee point voltage.
The formula for Knee Point Voltage is:
Vkp = K * If/CTR * (RCT + RL + RR)
in which,
K = Constant, conventionally taken as 2.0
Vkp = The minimum Knee Point Voltage
If = Maximum Fault Current at the location, in Amperes
CTR = CT Ratio
RCT = CT Secondary Winding Resistnace, in Ohms
RL = 2-way Lead Resistance, in Ohms
RR = Relay Burden, in Ohms
ugrasen.vishawakrma@gmail.com
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / gunasekaran
if it is 5P20 we can calculate from following formula
1.2*VA*ALF/rated secondary current.
magnetizing current it will be mA it may be .5 or .7 of current
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / savanth
Formula for vk is as follows
vk=if(rct+2*rl)
where if is fault current
rct is ct secondary resistance rl is lead resistance
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / yogesh
How to consider or calculate valu of Rct at the time of detail engineering???
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pradeep maurya
Dear friend,
Knee Point voltage is nothing but a point at which the CT
saturates. Thatsy its always better to design the CTs which
can operate without saturation even at a voltage appears in
the CT during fault condition. Pls find below the following
formula for calculating the Knee point voltage.
The formula for Knee Point Voltage is:
Vkp = K * If/CTR * (RCT + RL + RR)
in which,
K = Constant, conventionally taken as 2.0
Vkp = The minimum Knee Point Voltage
If = Maximum Fault Current at the location, in Amperes
CTR = CT Ratio
RCT = CT Secondary Winding Resistnace, in Ohms
RL = 2-way Lead Resistance, in Ohms
RR = Relay Burden, in Ohms
pkmauryain@gmail.com
| Is This Answer Correct ? | 0 Yes | 1 No |
what is KA rating and how can we choose switchgears on applications
1.what type of wave is produced from i.online ups ii.offline ups iii.inverter.why don't we use inverter instant of offline ups for computer,what's the reason?
it is possible to run 130V AC and 230 V AC cables run in same tray
How to know Resistance and Reactance value of main and aux winding of single phase capacitor start capacitor run induction motor to find capacitor value?
what should be the value of helathy insulation b/w two cores of LT cable.
i am working in a grid substation,TNEB having 13 yrs experience. Am I eligble to get apply for c licence now?
what is the use of spst switch in performing experiment on self excited dc motor?
how induction generator generated the power without excition like syncronous generator.
what the main difference of the 3 phase and 2 phase power supply??
How many devices can be connected in one zone of FACP
Dear sir, In our plant have Station Transformer having capacity,i want to know, why LV side 40 - 40MVA is given? & how we can get 6.3 KV supply from tertiary(i.e. Open delta connection), Vector Group YNyn0 - yn0 +d MVA Rating 80MVA / 40 - 40MVA + 26.7MVA Voltage rating 420 (Tap range +6,to -10)81.25% /11.5KV - 11.5KV +6.3KV
In a single how much maximum current and watts using
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)