can i use capillary type dp transmitter converted to
capillary type pressure transmitter. if i removed one side
capillary tube its work correctly?
Answer / k.sreenivasan
To begin with you must ask why there was a DP measurement
in the first place?
For example if you are measuring the DP across a Filter to
find filter choked condition, then removing one capillary
will defeat the basic concept.
If the DP xmr is used for a level measurement, then also
you will get wrong reading.
So unless you inform the details... correct answer cannot
be given.
By keeping one side of the transmitter open to atmosphere
by removing one capillary, the other side will read the
pressure with reference to atmosphere.
If you want vacumm pressure measurement then you have to
keep the HP side open and LP to the process. Vice versa for
gauge pressure measurement.
| Is This Answer Correct ? | 3 Yes | 1 No |
Yokogawa CENTUMVP R6.09 unable to download to Engineering Station with ExaOPC R3.75 The issue is when I try to download the common project section to the Engineering Station (STN) from the HIS in System View, it is unable to connect. The error displayed is: WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. STN0149 ---- ERROR = 2 WARNING = 1 ---- Background: >Updated the ExaOPC software on the STN from 3.60 to 3.75 >STN operating system is Windows Server 2008 R2 >HIS operating system is Windows Server 2016 Stanard Solutions attempted include: >Ensuring all IP addresses are correct and all networked devices can be pinged. >The ability to ping a device using its host name from another device (<ping STN0149> from HIS) >Ensure both devices firewalls are disabled. >The antivirus installed on the STN is disabled. >Ensuring both devices are within the same workgroup. >Added both devices to each other's Host and LMHost files. >Running IT Security tool after changing any administrative settings.
What are primary elements of measuring pressure?
What is re-latch the manual trigger in solenoid valve
0 Answers Valvitalia Systems Division,
What are the key components of control loop?
An electronic p controller has an input range of 1-5v, and output range of 4-20mA, while testing a step change of 0.4 was applied at the input , the PB setting was 50% ,what should be the change in the output ?
How does a redundant controller comes in line when the main controller fails??
2. What is ultrasonic flowmeter?
what is function of DCS , and how is it work , explain with difination
1 Answers Bapco Bahrain Petroleum Company,
calculate the rane of level use of this values, h=3 meter density=0.9 , whats the rang?
We are used CENTUM CS3000 of YOKOGAWA. please tell me how to simulate wihtout FCS and vnet.
what is use of communication wire in multipare cable(oil and gas field), why this communication wire not used in single pair cable?
Why we use DPT? can we use PT instead of DPT?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)