can i use capillary type dp transmitter converted to
capillary type pressure transmitter. if i removed one side
capillary tube its work correctly?
Answer / k.sreenivasan
To begin with you must ask why there was a DP measurement
in the first place?
For example if you are measuring the DP across a Filter to
find filter choked condition, then removing one capillary
will defeat the basic concept.
If the DP xmr is used for a level measurement, then also
you will get wrong reading.
So unless you inform the details... correct answer cannot
be given.
By keeping one side of the transmitter open to atmosphere
by removing one capillary, the other side will read the
pressure with reference to atmosphere.
If you want vacumm pressure measurement then you have to
keep the HP side open and LP to the process. Vice versa for
gauge pressure measurement.
| Is This Answer Correct ? | 3 Yes | 1 No |
Basic working principle of control valves
why would you like to join our company
in i/o panel for digital ouput(do) how much power(in volts) we must give?
HOW TO DO PERFECT CALIBRATION OF DIFFERENTIAL PRESSURE TRANSMITTER FOR CLOSE VESSEL TANK LEVEL PURPOSE ???? AND HOW TO MAKE ZERO PRESSURE ?? Rosemount 2051 Pressure Transmitter with HART® Revision 5 and 7 Selectable Protocol BIENG USED !! HOW TO CALIBRATE FIELD SIDE DPT WITH THE HELP OF SPAN & ZERO PUSH BUTTONS ??
if the neutral and ground of ups voltege are connected together in the source itslef then why the voltege b/w neutral and ground comes positive in some other destination inspite of having earth pit. how can we mimmise this?
difference between accuracy and precision
whats the diff b/w zero pressure and obsolute pressure
How to calibrate DP tramitter in flow measurement application? consider my range of flow is 0 to 2000 kg/hr ? please give calculation of , How much pressure applied on low pressure side and high pressure side please give detail of calculation .... It so important for me please reply as soon as possible
What is the maximum operative of Drive ?
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used? Please tell me its Calculation formula.
please send the sample qustion paper for iocl written test ..
what is the difference between hub and switch?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)