How to Calibrate Transducers? Can you give me a step by ste
procedure?
Answer / mahesh bajaj
The transducers are calibrated against reference standards
which are atleast 10 times more accurate then the transducer
to be calibrated.
Let me elaborate by giving an example.
Orifice plate infers flow rate by measuring differential
pressure.so to calibrate orifice plate, reference standard
say magnetic flowmeter is used which measures flow rate.say
flow range is 0-100 lpm and at every 10 lpm, differential
pressure across orifice is measured and constant is evolved
between flow rate and differential pressure. This constant
is also known as discharge coefficient or calibration
constant and one dimensional bernolli's equation is used to
compute this constant.
Now once you know the constant the orifice flow element is
ready to be used in any line size without using any
reference standard.
Hope this helps.
Is This Answer Correct ? | 7 Yes | 1 No |
What is input and output of plc & dcs
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
PT RTD Range: -200 to 500 degree celsius If I configured in DCS Lower range and Upper range . In face plate it shows red colour due to overa range how was the characteristics look If the temperature is more than operating range. how was the characteristics look . whether its in Resistance vs Temperature curve is Linear or Non linear
Why we. Don't measure current in parallel? Why we measure current in series and why we measure voltage in parallel only?
2 Answers Almeer Technical Services,
Is an analogue only transmitter as accurate as a smart transmitter?
why we use the ac supply load cell>?can we use the dc supply load cell?advantages and disadvantage of the ac supply load cell?
Explain Difference between Bech set and operating range of control valve
What is open loop checking and close loop checking
How to calibrate displacer type level transmitter (chemtrol make )for level measurement in hotwell , LP & HP heater ?
what is the deference bitween DCS and PLC SCADA HMI System for Power Process Industry.
how we can measure the interface level?is it possible to measure interface level with dp or pressure transmitter?
give eg of how I/P is used in control loops