yogokowa field bus system transmitter all's we are geting
IOP fault in Contiunes please help me fine how we can
normal the broblems?
Answers were Sorted based on User's Feedback
Answer / nileshkumar jambukiya
1)IOP means input open, when process velue (PV) is out of
renge (20 ma) then IOP alrm comes,
2)when PV is small then minimum range (LRV) less then 4ma
then IOP- alrms come,
3)when cable short or open from loop then same alarm come
iop-,
Is This Answer Correct ? | 33 Yes | 3 No |
IOP Faults are very common in any Yokogawa Fieldbus setup.
As rightly stated in Ans 1, it means Input Open. The idea here is that there is an open circuit somewhere. The circuit here may be the physical circuit or the logical circuit. By logical circuit, I mean the control drawings.
Now lets look are typical scenarios and solutions:
1. Transmitter input over ranged: For a transmitter that is supposed to transmit up to 100%, if its getting a 110% input, it goes on IOP (+) but you will not see the + most times. Under ranged transmitter would give IOP-.
Solution: Get the transmitter input back to the normal range.
2. Consider a control loop with a transmitter input to a controller. whenever the transmitter fails, the controller will give an IOP fault i.e reporting that its input is open - in this case, check the transmitter and possibly change it if bad.
3. Sometime control valves give IOP when they are faulty.
4. Loop component failures can also cause IOP. Check components like the Mega blocks, connectors etc
In general, initial troubleshooting will be re-downloading the control drawing. You can also perform reconfiguration of the Fieldbus devive.
Hope this clarifies.
Osagie.
Is This Answer Correct ? | 6 Yes | 0 No |
1) Infield bus system, IOP detection is different from HART system.
2) IOP will occur only for input e.g. transmitters.
3) One probability is there (which is most common) that your transmitter is under-ranged or PV value fluctuates highly (on wither ends). Being s digital system you will not receive IOP(-) in FF system.
4) Check for alarms and run integrity test (via PRM) and check if any of the internal blocks like AI or Transducer block or Resource Block is going to OOS (Out of service or Manual Mode).
5) Additional Check :
Check if you are receiving CNF error. If it comes then you may reset the transmitter by removing the power or isolating it from Loop.
This shall resolve the error. If not then you need to replace the transmitter.
Hope this helps.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abdulcader
FF device signal is a communication signal.If any noise or jetter valve are high.it will affect the total segment and time to time particular segment's all devices will go iop.
We can diagnosis the problem by using FFADM[FFadvanced diagnosis module] or fieldbus monitoring device FBT6.
Mostly diagnosis noise valve high in barrier.If you replace the barrier 90% problem will solve.
Is This Answer Correct ? | 2 Yes | 0 No |
what is the path to communicate from profi to ofc.what is the means of communication.what is multi cire cable in ofc.
is manifold required for an integral orifice meter?
I have applied the post Junior Engineer-(TM)in R.R.B CHANDIGARH recently . what type of question i have to practice and which book ?. can i get any model question paper?
How to find out the current of two motors having same power consumption but different RPM?
In case of Transmitter's(e.g.Ultrasonic Flow meter ) we have an normal practise of selction of upstream and downstream distance such as (20D and 5D ).can anyone please let me know whow to calculate "D" ?? i guess it refers to pipe thickness is t right ?
I saw one P&ID 6" control valve has been connected with 8" process line, and 2" valve also connected in parallel with 6" valve. why the 2" valve connected in parallel, Is there any technical reason. please clarify. With Regards-Kittu
What is the full form of PMMC ?
why can't we use 5-20mA standard or some other instead of 4- 20mA?
please tell me five types of fault of control valve and positioners?please
explain the working of Coriolis Flowmeter.
can you suggest good traning institute in instrumentation ? (in automation, or designing)
How a oxygen sensor & analyzer work at boiler or furnace, what’s the principle & science is beyond this, How O2 sensor scene & convert signal & move toward analyzer & analyzer show reading in percent?
1 Answers GS Engineering Construction, KNIC,