Answer / nileshkumar jambukiya
1)IOP means input open, when process velue (PV) is out of
renge (20 ma) then IOP alrm comes,
2)when PV is small then minimum range (LRV) less then 4ma
then IOP- alrms come,
3)when cable short or open from loop then same alarm come
iop-,
| Is This Answer Correct ? | 33 Yes | 3 No |
IOP Faults are very common in any Yokogawa Fieldbus setup.
As rightly stated in Ans 1, it means Input Open. The idea here is that there is an open circuit somewhere. The circuit here may be the physical circuit or the logical circuit. By logical circuit, I mean the control drawings.
Now lets look are typical scenarios and solutions:
1. Transmitter input over ranged: For a transmitter that is supposed to transmit up to 100%, if its getting a 110% input, it goes on IOP (+) but you will not see the + most times. Under ranged transmitter would give IOP-.
Solution: Get the transmitter input back to the normal range.
2. Consider a control loop with a transmitter input to a controller. whenever the transmitter fails, the controller will give an IOP fault i.e reporting that its input is open - in this case, check the transmitter and possibly change it if bad.
3. Sometime control valves give IOP when they are faulty.
4. Loop component failures can also cause IOP. Check components like the Mega blocks, connectors etc
In general, initial troubleshooting will be re-downloading the control drawing. You can also perform reconfiguration of the Fieldbus devive.
Hope this clarifies.
Osagie.
| Is This Answer Correct ? | 8 Yes | 0 No |
1) Infield bus system, IOP detection is different from HART system.
2) IOP will occur only for input e.g. transmitters.
3) One probability is there (which is most common) that your transmitter is under-ranged or PV value fluctuates highly (on wither ends). Being s digital system you will not receive IOP(-) in FF system.
4) Check for alarms and run integrity test (via PRM) and check if any of the internal blocks like AI or Transducer block or Resource Block is going to OOS (Out of service or Manual Mode).
5) Additional Check :
Check if you are receiving CNF error. If it comes then you may reset the transmitter by removing the power or isolating it from Loop.
This shall resolve the error. If not then you need to replace the transmitter.
Hope this helps.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abdulcader
FF device signal is a communication signal.If any noise or jetter valve are high.it will affect the total segment and time to time particular segment's all devices will go iop.
We can diagnosis the problem by using FFADM[FFadvanced diagnosis module] or fieldbus monitoring device FBT6.
Mostly diagnosis noise valve high in barrier.If you replace the barrier 90% problem will solve.
| Is This Answer Correct ? | 2 Yes | 0 No |
why we cant transmit the dc current easily
what is the use of conrol cable..?
what is the diffrence between pressure safety valve & pressure relief valve....pls
Yokogawa dcs normally where will change 4-20 MA to DC voltage( node or I/o cards?)
What is heating effect?
0 Answers Process Control Technologies,
thru which signal does µP communicate with memory
how to calibrate an error for pressure transmitter, make it easy to understand
What are the different types of temperature sensors and the principle they work on?
What Is Pre- Commissioning Package +what is DCS & ESD Pre- Commissioning for Instruments Please explain your answer on practical ground base
Decibel.
Draw a simple circuit for a well head control panel used to protect the well against fire, leak, blockage, ESD, & controls the operation of one downhole & one surface safety valve. Explain the operation and controls
what is the difference between Ethernet unmanaged and managed Switch?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)