yogokowa field bus system transmitter all's we are geting
IOP fault in Contiunes please help me fine how we can
normal the broblems?
Answers were Sorted based on User's Feedback
Answer / nileshkumar jambukiya
1)IOP means input open, when process velue (PV) is out of
renge (20 ma) then IOP alrm comes,
2)when PV is small then minimum range (LRV) less then 4ma
then IOP- alrms come,
3)when cable short or open from loop then same alarm come
iop-,
| Is This Answer Correct ? | 33 Yes | 3 No |
IOP Faults are very common in any Yokogawa Fieldbus setup.
As rightly stated in Ans 1, it means Input Open. The idea here is that there is an open circuit somewhere. The circuit here may be the physical circuit or the logical circuit. By logical circuit, I mean the control drawings.
Now lets look are typical scenarios and solutions:
1. Transmitter input over ranged: For a transmitter that is supposed to transmit up to 100%, if its getting a 110% input, it goes on IOP (+) but you will not see the + most times. Under ranged transmitter would give IOP-.
Solution: Get the transmitter input back to the normal range.
2. Consider a control loop with a transmitter input to a controller. whenever the transmitter fails, the controller will give an IOP fault i.e reporting that its input is open - in this case, check the transmitter and possibly change it if bad.
3. Sometime control valves give IOP when they are faulty.
4. Loop component failures can also cause IOP. Check components like the Mega blocks, connectors etc
In general, initial troubleshooting will be re-downloading the control drawing. You can also perform reconfiguration of the Fieldbus devive.
Hope this clarifies.
Osagie.
| Is This Answer Correct ? | 8 Yes | 0 No |
1) Infield bus system, IOP detection is different from HART system.
2) IOP will occur only for input e.g. transmitters.
3) One probability is there (which is most common) that your transmitter is under-ranged or PV value fluctuates highly (on wither ends). Being s digital system you will not receive IOP(-) in FF system.
4) Check for alarms and run integrity test (via PRM) and check if any of the internal blocks like AI or Transducer block or Resource Block is going to OOS (Out of service or Manual Mode).
5) Additional Check :
Check if you are receiving CNF error. If it comes then you may reset the transmitter by removing the power or isolating it from Loop.
This shall resolve the error. If not then you need to replace the transmitter.
Hope this helps.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / abdulcader
FF device signal is a communication signal.If any noise or jetter valve are high.it will affect the total segment and time to time particular segment's all devices will go iop.
We can diagnosis the problem by using FFADM[FFadvanced diagnosis module] or fieldbus monitoring device FBT6.
Mostly diagnosis noise valve high in barrier.If you replace the barrier 90% problem will solve.
| Is This Answer Correct ? | 2 Yes | 0 No |
which is the best type to measure level of a Tank(water). Displacer or Differential Pressure method?
what is the working principle of dis-placer type level transmitter
WHAT IS TMXT IN TEMPERATURE FOUNDATION FIELDBUS.
in split range control valve,two valve should be in two different line and that should have some distance,and we have only one positioner feed back link.so how we connect one feed back in two control valves?if you have picture please forward me.my email id kb.syamkumar@gmail.com
need to calculate flow rate with the help of dp range and orifice bore dia and size. range is 0 to 400 inwc and orifice size is 12 inch 150 # rf and bore dia is 7.180 inch. need to calculation for flow rate
T.x range -0.1 to 0.2 milibar,so how much mili ampear at 0.1 milibar?
Why grounding is necessary? Give example with diagram.
0 Answers Bright Point, DS Group,
Why do we have earthing cable in branch cable and shield in the same cable?
0 Answers Process Control Technologies,
What are the difference between mass flow meter, magnetic flow meter and vortex flow meter.
How ejector(or)evactor air pump is working in thermal power plant?
when the force applied on load cell the ohms will be varriying .and how its convert ohms to mv generate and have any formulae?
1 Answers UETCL Uganda Electricity Transmission Company Limited,
A length of steel pipe is used to carry sea water to a desalination plant. An adequate corrosion allowance must be specified and indicated in the piping specification, which affects the _________________________ of the pipe
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)