why the capacity of power plant is given in MW though the
generators are rated in MVA?
Answers were Sorted based on User's Feedback
Answer / lalit
if we talk about the generator then we have to classify the
active power as well as reactive power i.e. V*I because the
reactive power is also used in generator for the excitation
purpose( for flux production). hence its rated as MVA in
other hand, for power transmission only active power is used
i.e. VICos theeta. hence its rated as Mw.
| Is This Answer Correct ? | 5 Yes | 0 No |
The capacity is decided by prime mover
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / koteswararao
In generator to generate the reactive power in combination of voltage and current base so it ishaving both specification in MVA in plant capacity is combination of reactive power and power factor. how much load taken byplant.
| Is This Answer Correct ? | 3 Yes | 7 No |
A circuit breaker is a
why in an electrical lab a bulb connected to supply goes off slowly when the main supply is switched off?
what is the difference between VARIAC,AUTO TRANSFORMER,DIMMERSTAT.
i completed my b.tee(eee) in 2009, but i did not join any job, i joined in my father business, now i want to join any good job, please suggest any course for me
what type of oil is used in transformers? a)conduting b) insulating
25 Answers ABB, LGS,
why the earth conductor in top of the tranmission line ?
I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.
Which type of DG need Netral Earthing?
what is carona and how is occur?
10Hp, 3-phase, 415v, 50Hz induction motor. The above motor is to run on Star-Delta connection, so how do i make following hardware selection 1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current or Line Current), 4) OLR, Please tell in detail how to do the above, so as to get the ans. of it even if the Hp rating changes.
In our plant we have installed new MCC with ELR and CBCT which is detecting some leakage current in the system but it leading to some confusion when to check that in which feeder which is drawing current we put off the whole panel itself but still CBCT detecting some leakage current so can anybody ans me , where i am going wrong or how to detect whether its actual leakage or CBCT malfunctioning.
if two transformers are placed parallel & both have fault impedance of 50KA will it increase or decrease show example?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)