What is correction factor in Tan delta test?
on site the ambient / atmp temperature is different.
whereas the facotry test conducted may be at different
temp .
As such to compare the value we apply a correction factor
such that the values are converted to a std test
temperature and we can have a comparsion of the obtained
results.
Is This Answer Correct ? | 4 Yes | 3 No |