in our sub station why we step down firstly 33kv\11kv then
11kv to 430v. can we direct step down 33v to 430.v.
Answers were Sorted based on User's Feedback
Answer / arun
yes. by using step down transformer (33Kv to 430V
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / jeff
yes you can, normally they use 33kv/11kv tranformer because
the side have more than 2 sustation and need more
transformer, for the 33/.433kv transformer is expensive
than 11/.433 transformer. so they just step down the HT
33KV to 11KV first than supply to two substation by using
11/.433kv transformer
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / engineering.force
One more important point you all have missed is about the
secondary winding current. If we step down from 33/11 KV the
secondary current will be less than if we step down from 33
KV/440 V, hence the secondary winding has to be accomodated
with above high value of current. This will lead to increase
in winding diameter, thus increasing the overall size of the
transformer, and also increase in the heating of the
secondary, thereby reducing the efficiency of the
transformer. And hence costly. So taking in the above
considerations, we have to design the step down voltage
level so as to make it cost effective and economical.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / puneet kulshreshtha
IN PAST MANY OF TIMES WE USE 33/.430 KV S/S
BUT IT IS VERY EXPENSIVE SO WE USE 11/.430 S/S FOR EASY
COST AND TRANSPORTATION
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / gsamguna
we can use 33kv/ 440 transformer
who said cannot
if u want 33kvto 440 u want to install two transformer
33kv/11 and 11/440v
this s stupit answer ..
sure we can use 33kv/ .44 kv directly step down
| Is This Answer Correct ? | 0 Yes | 1 No |
it will be dangerous as the transformers which converts 11
kv to 430 volts cant be installed in colonies
| Is This Answer Correct ? | 0 Yes | 8 No |
How relay works, reverse relay, master relay, os relay, earth fault relay and what is its setting point
which is the most common harmonics 3rd,5th,7th affect the systegm
what is rotating transformer? what is the uses of it?i mean applicaitons?
What is the types of HT motor testing
WHY TRANSFORMER RATING IS MENTIONED IN KVA RATHER THAN KW
Explain the experiment on ward leonard method of a speed control on a dc shunt motor with an suitable circuit diagram.
what is acceptable leakage current for 33kv cable while doing high voltage test for cable? how to calaulate the leakage current for 33kv or any rated cable?
Whether the vacuum contactor requires Short circuit protection?If No,why?
What is The function of tvm(tri-vector meter)??
what is the diffrence between resistive , inductive and capactive load please explain with exmpels?
Why the efficiency of generator is more than motor in swinburne's test
explain Xmer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)