Can 2 nos. of 1 ton split ac be used through a 20 am supply
meter?
Answers were Sorted based on User's Feedback
Answer / gskasherwal
yes 1ton split ac having 1.2 kw power so 1.2*2=2.4 kw which can be used on single phase meter.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / s.ghosh
The answer is "Yes" for steady state current, but "No" for
starting current. You can use the 20A capacity line for 2
nos. 1T AC, but you have to ensure that at no instance, both
the ACs are switched on simultaneously.
| Is This Answer Correct ? | 0 Yes | 1 No |
whenewher three phase supply is given to induction motors revolving/rotating field is created & rotor rotates.When the three phase supply is given to three phase transformer then revolving,/rotating field is created or not? if not why?
why transmiision rating in kva?
in transfomer which type of oil is use!
why ct secondary side shortlink provided? its open what will happen?while running ?
what is shunt trip coil? what was the function in rmu?
why white color LED light is not possible?
what is the avr
6 Answers ArcelorMittal, Heidelberge Cement,
what is EBXl (electron beam cross linked ) cable ?
What is meant by inverse definite mean time (IDMT)& definitemean time (DMT)?
If AVR fails in DG set what will be the affect?
17 Answers GoodYear, Hotline Glass, HSL,
What will happen if 33 kv is given to a 11/0.415 kv Distribution transformer?
what is softstarter? explain briefly where it is used?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)