meter ratio is 100/5 CT ratio is 125/5, when the ratios changes i.e., CT ratio is 125/5 meter ratio is 100/5 what is the MF in boths conditions?
Meter 100/5 A ,and Ct 125/5 . For 100A load current the CT secondary current is 4A which is taken as '80A load current 'by the meter . Hence M.F. is 125/100 or 1.25
Is This Answer Correct ? | 0 Yes | 0 No |
How to calculate PF capactors for a connected load?
how to calculate the megger values for motors and cables?
transformer phasor diagram under load explain it?
what is the difference between DOL starter&star-delta starter& automatic star-delta starter
HI, I want to buy a new Xformer to my plant. what are the main parameter should I check ( Xformer rating is 16 MVA)
what do you mean by type zero control sytem ?Give an practical example of type zero contol sytem?
friends., why celling fan rotate cockwise direction and wall fan anticickwise direction ?
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.
What is PIR (pre inserting resistance) in 400kv EHV SF6 BREAKER? Why it use?
When do you use a VFD motor?
why v use only sodium bulb or orange color lights on streets, y nt CLF OR TUBE LIGHTS
state the construction of incondenscent lamp?