what is the function of generator exciter
Answers were Sorted based on User's Feedback
Answer / sivasamy k
Exciter is providing DC supply to AC Gen Rotor,the DC
supply is improving the magnetic flux density in AC Gen.So
your Generating voltage is rised ,which is upto your rated
voltage.
| Is This Answer Correct ? | 114 Yes | 22 No |
Answer / rakesh
exciter is giving dc source to the stator field windings
in case of generators
if we give dc source what will happen is create constant
magnetic field around electromagnets
so whenever rotating conductor cuts the magnetic field the
emf will be induced ,this emf have collected conductor bars
so power is produced
exciter main function is maintaining constant dc source
| Is This Answer Correct ? | 38 Yes | 17 No |
Answer / muhammad zafar iqbal(uet lahor
Excitor produces AC suply which is converted into DC by means of retifier or simply diode bridge.This DC is provided to rotor magnetic field winding producing stong field because DC peak value is high and it is constant.Thus induces Current in the stator armature conductors.In this way,exciter excites the
Generator
| Is This Answer Correct ? | 19 Yes | 5 No |
Answer / mohit parmar
exciter gives the DC supply to the rotor of the ggenerator
developing a magnetic field,with the help of exciter we can
also vary the pf and voltage level of generator.
| Is This Answer Correct ? | 28 Yes | 19 No |
Answer / nalla
the function of exciter is to generate the rotor magnetic field and thus control the terminal voltage of the Generator and also to vary the MVAR output of the Alternator.
| Is This Answer Correct ? | 14 Yes | 6 No |
Answer / roberto c. abejo
There are two types of exciters. STATIC and ROTARY Exciters. The function of an exciter is to supply the excitation DC voltage of the fixed poles of Generator. and or the function of all exciters is to enable a voltage regulator or other control device to use a control signal to adjust the much larger of generator field current. In essence, the exciter is a power amplifier.
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / rca
the function of exciter is to supply the excitation DC voltage of the fixed poles of the generator.
| Is This Answer Correct ? | 2 Yes | 5 No |
if 6 earth pit value is 1.5 ohm then what should be the number of earth pit to make the value .8 ohm
To prevent the mal operation of a differentially connected relay while energizing a transformer, the relay restraining coil is baised with (a)second harmonic current (b)fifth harmonic current (c)third harmonic current (d)seventh harmonic current
what is the differance of acb and mcb and mccb
What shocks us , Current or voltage?
ELECTRICAL MACHINE
how is control wiring coding is done in a CRP panel ?
0 Answers Genus, Havells, Hindustan Power Projects,
What is the fusing factor ?
4 Answers MESCOM Mangalore Electricity Supply Company Limited,
Why the transformers are rated in KVA. ? in new view.
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
how to select electrical equipment such as fuse,dg,transformer,motor,msb,wire,cable as per the connecting load..please mention any books to design,take licence
0 Answers Gujarat Electricity Board,
What is the current carrying capacity of 0SWG,3SWG,10 & 12 SWG solid bare overhead copper conductors?
how is differential relay working in transformer.comparison with generator defferntial relay
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)