How to check vortex flow meter is in good condition while
we do not having calibration setup?
Answers were Sorted based on User's Feedback
Answer / krishna reddy
Let me know first which make you have.
Instrument have min and max ranges on its name plate.
So wiht multimeter you can check 4-20ma of flow meter.It
must be 4 ma if flow is zero and 20ma if flow is max range.
supose your flow mete got 100L/hr.
for 4ma flow should be 0 L/hr
8ma - 25L/hr
12ma - 50L/hr
16ma - 75L/hr
20ma - 100L/hr
Like this you can check.
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / amit
U can do the cold test by checking the sensor.It has piezo
sensors in symetrical manner. U can check both piezo
sensor by checking the capacitance. If capacitance is
accordance with size means sensor is OK. same way u can
check temp and pressure sensor(by checking the resistance)
if it has.This way u can check the healthiness of the
sensor. If u want to check the response of sensor, u can
give little vibration to the sensor by hammering on it and
check the response on transmitter. U cannot directly check
the calibration for flow on field itself.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / tuhin
@soumil: no hp and lp side exist in vortex flowmeter. Vortex
principle is different.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / saumil
In this meter hp or lp any one side we isolate line valve and check zero if it is ok then meter is ok
Is This Answer Correct ? | 1 Yes | 3 No |
Can we use twisted pair cable instead of ethernet for communication?
there are two candidates p and q in an election.During the campaign,40% of the voters promised to vote for P ,and rest for Q.however, on the day of election 15% of the voter went back on their promise to vote for P and instead voted for Q. 25% of the voters went back on their promise to vote for Q and instead voted for P.suppose,P lost by two votes,then what was the total no. of voters.
I have a close vessel tank which is under vaccum when in running condition so pl. Provide it's range for dp type tx whose flange to flange distance is 440 mm and density is 1
What are the maximum packet size of: a) HART b) Profibus DP c)Profibus PA d) DeviceNet e) Foundation Fieldbus
who to convert dc to ac
Can be operate control valve without positioning if yes ? how and why?
What is input and output of plc & dcs
What is the reason PT speed not incresed in gas turbine?
in the flow caluclation k value how to caluclate.mass flow & volum flow.
How we select the range of level transmitter in closed vessel ?
Differentiate between PLC, SCADA and DCS systems
1 Answers Mumias Sugar, SRF, Trimula Industries,
What is Vena contracta?