How to check vortex flow meter is in good condition while
we do not having calibration setup?
Answers were Sorted based on User's Feedback
Answer / krishna reddy
Let me know first which make you have.
Instrument have min and max ranges on its name plate.
So wiht multimeter you can check 4-20ma of flow meter.It
must be 4 ma if flow is zero and 20ma if flow is max range.
supose your flow mete got 100L/hr.
for 4ma flow should be 0 L/hr
8ma - 25L/hr
12ma - 50L/hr
16ma - 75L/hr
20ma - 100L/hr
Like this you can check.
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / amit
U can do the cold test by checking the sensor.It has piezo
sensors in symetrical manner. U can check both piezo
sensor by checking the capacitance. If capacitance is
accordance with size means sensor is OK. same way u can
check temp and pressure sensor(by checking the resistance)
if it has.This way u can check the healthiness of the
sensor. If u want to check the response of sensor, u can
give little vibration to the sensor by hammering on it and
check the response on transmitter. U cannot directly check
the calibration for flow on field itself.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / tuhin
@soumil: no hp and lp side exist in vortex flowmeter. Vortex
principle is different.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / saumil
In this meter hp or lp any one side we isolate line valve and check zero if it is ok then meter is ok
Is This Answer Correct ? | 1 Yes | 3 No |
Explain the burnout feature.
how to make temperature closed loop
I am using Capacitive type level transmitter for measuring oil level in a closed tank (lub oil tank). The txs range is 1500mm, and they do hunt regularly (for about 45mm), can anybody tell what could be the reason??? or any other type level tx that could be used to avoid this?
What are the key features of a Distributed Control System? describing the various layers (sensor through to business system interfaces) as well as the hardware, software and security aspects of the DCS.
I am working in a process industry, in that there are several sections devided in the SCADA screens and individual sections may START independently. But sometimes i am facing problem i.e, if section 2 Stopped by the operator immediately Section 1 or Section 3 or Section 4 is getting stopped can you expain the reason behind this?
Briefly describe instrumentation job
WHAT IS THE VALUE OF MICRON
what is the diffrence between LCN and UCN
why metallic housing is provided of solenoid valve.
yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help me fine how we can normal the broblems?
p=hdg,please explain these parameters?
what should be minimum length and size of impulse line for steam flow orifice and feed water orifice? asked by sanjay parihar