Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to check vortex flow meter is in good condition while
we do not having calibration setup?

Answers were Sorted based on User's Feedback



How to check vortex flow meter is in good condition while we do not having calibration setup?..

Answer / krishna reddy

Let me know first which make you have.

Instrument have min and max ranges on its name plate.
So wiht multimeter you can check 4-20ma of flow meter.It
must be 4 ma if flow is zero and 20ma if flow is max range.
supose your flow mete got 100L/hr.
for 4ma flow should be 0 L/hr
8ma - 25L/hr
12ma - 50L/hr
16ma - 75L/hr
20ma - 100L/hr

Like this you can check.

Is This Answer Correct ?    10 Yes 3 No

How to check vortex flow meter is in good condition while we do not having calibration setup?..

Answer / amit

U can do the cold test by checking the sensor.It has piezo
sensors in symetrical manner. U can check both piezo
sensor by checking the capacitance. If capacitance is
accordance with size means sensor is OK. same way u can
check temp and pressure sensor(by checking the resistance)
if it has.This way u can check the healthiness of the
sensor. If u want to check the response of sensor, u can
give little vibration to the sensor by hammering on it and
check the response on transmitter. U cannot directly check
the calibration for flow on field itself.

Is This Answer Correct ?    1 Yes 0 No

How to check vortex flow meter is in good condition while we do not having calibration setup?..

Answer / tuhin

@soumil: no hp and lp side exist in vortex flowmeter. Vortex
principle is different.

Is This Answer Correct ?    0 Yes 0 No

How to check vortex flow meter is in good condition while we do not having calibration setup?..

Answer / saumil

In this meter hp or lp any one side we isolate line valve and check zero if it is ok then meter is ok

Is This Answer Correct ?    1 Yes 3 No

Post New Answer

More Instrumentation Interview Questions

I WANT TO KNOW SOME BASIC CONCEPTS RELATED TO INSTRUMENTATION

4 Answers  


WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?

8 Answers  


why 8bit microprocessor referred as 2^16?

2 Answers  


7. What are tri-state devices and why they are essential in a bus oriented system

1 Answers  


Why some transmitter shows flow in MMWC and some in TPH?

2 Answers  


How to consider the flow directions for control valve (Globe) Is the there any easy understanding in order to select the flow directions?

3 Answers  


What is inside the PLC panel? How does instruments communicate to DCS computer via PLC? What is the type of wiring in PLC connections? Please answer... Thanks

1 Answers  


I have a orifice installed in plant which is design for 0~100 inH2O for 0~80MMSCFD, now due to process change the maximum flow is change to 120 MMSCFD so for this new process value what will be the DP across orifice.

1 Answers  


Good Evening all.My question is - For a feed water line to an equipment if i need to measure the flow we will use orifice /magnetic/vortex depend on cost/spec.If i need to measure a ''Alarm''signal and ''Interlock'' from one point i think we can use orifice type in one location with 2 different tapping points - one for alarm and one for an interlock to flow valve..If in case i need to have both these signals(Alarm & interlock) from magnetic flow meter,is it possible??will 2 seperate sensors will be located inbuilt r we can program it ??..i thk we can have one transmitter with these 2 signals...need to know any technical issues are there?pls clarify

3 Answers  


what is the use of glycol filling in seal pot (or) condensate pot in instrument impluse line?

7 Answers  


Regarding , there is an air cooler which control the fans(50% of AV FANS) by temperature in outlet , and the louver of Air cooler is controlled by HIC from control system , So if on Air cooler we will consider 2 individual I/P converter or positioner?

0 Answers   Chagalesh Consulting Engineers,


how to know the URL and LRL for steam drum level and why the calibration range is in negative ?

1 Answers   JSW, Samsung,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)