How to check vortex flow meter is in good condition while
we do not having calibration setup?
Answers were Sorted based on User's Feedback
Answer / krishna reddy
Let me know first which make you have.
Instrument have min and max ranges on its name plate.
So wiht multimeter you can check 4-20ma of flow meter.It
must be 4 ma if flow is zero and 20ma if flow is max range.
supose your flow mete got 100L/hr.
for 4ma flow should be 0 L/hr
8ma - 25L/hr
12ma - 50L/hr
16ma - 75L/hr
20ma - 100L/hr
Like this you can check.
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / amit
U can do the cold test by checking the sensor.It has piezo
sensors in symetrical manner. U can check both piezo
sensor by checking the capacitance. If capacitance is
accordance with size means sensor is OK. same way u can
check temp and pressure sensor(by checking the resistance)
if it has.This way u can check the healthiness of the
sensor. If u want to check the response of sensor, u can
give little vibration to the sensor by hammering on it and
check the response on transmitter. U cannot directly check
the calibration for flow on field itself.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / tuhin
@soumil: no hp and lp side exist in vortex flowmeter. Vortex
principle is different.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / saumil
In this meter hp or lp any one side we isolate line valve and check zero if it is ok then meter is ok
| Is This Answer Correct ? | 1 Yes | 3 No |
How to calculate P,I&D value in PID controller ?
0 Answers Jindal Steel and Power, SAL Steel Power,
Why Instrumentation Air Compressor called as Instrumentation Air compressor?pls dont just tell its trasferring IA to all transmitter,valves.I need exact reason, please......................
what will be the principle & application of dissoled oxygen analyzer at wast water treatment plant at oxidation basin & how it work?
Describe a time when you anticipated potential problems and developed preventive measures.
Describe how to use megger to measure the earth resistance and insulation resistance
where is a level displacer is used?
how to replace the smart transmitter software
why pneumatic control signal output is use 0.2 to 1 kg/cm2
what is the procedure for auto tune in masoneialn 12300 series displacer type transmitter?
in transmiters(rose mount) how to check output 4-20ma ? and input 24v? i need exact explanation?
please give me the syllabus and sample questions if possible for Instrumentation for Vizag Steel plant MT (Trainee) 2009 exam
1 Answers Pedvak, Steel Plant, Vizag Steel,
how can leve transmetter calibate in feild .and also put cv and flow plz .....
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)