Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to check vortex flow meter is in good condition while
we do not having calibration setup?

Answers were Sorted based on User's Feedback



How to check vortex flow meter is in good condition while we do not having calibration setup?..

Answer / krishna reddy

Let me know first which make you have.

Instrument have min and max ranges on its name plate.
So wiht multimeter you can check 4-20ma of flow meter.It
must be 4 ma if flow is zero and 20ma if flow is max range.
supose your flow mete got 100L/hr.
for 4ma flow should be 0 L/hr
8ma - 25L/hr
12ma - 50L/hr
16ma - 75L/hr
20ma - 100L/hr

Like this you can check.

Is This Answer Correct ?    10 Yes 3 No

How to check vortex flow meter is in good condition while we do not having calibration setup?..

Answer / amit

U can do the cold test by checking the sensor.It has piezo
sensors in symetrical manner. U can check both piezo
sensor by checking the capacitance. If capacitance is
accordance with size means sensor is OK. same way u can
check temp and pressure sensor(by checking the resistance)
if it has.This way u can check the healthiness of the
sensor. If u want to check the response of sensor, u can
give little vibration to the sensor by hammering on it and
check the response on transmitter. U cannot directly check
the calibration for flow on field itself.

Is This Answer Correct ?    1 Yes 0 No

How to check vortex flow meter is in good condition while we do not having calibration setup?..

Answer / tuhin

@soumil: no hp and lp side exist in vortex flowmeter. Vortex
principle is different.

Is This Answer Correct ?    0 Yes 0 No

How to check vortex flow meter is in good condition while we do not having calibration setup?..

Answer / saumil

In this meter hp or lp any one side we isolate line valve and check zero if it is ok then meter is ok

Is This Answer Correct ?    1 Yes 3 No

Post New Answer

More Instrumentation Interview Questions

Why in turbine used two critical speed band ?

1 Answers   Ankit Metal Power,


in a power plant which system are compensated?

2 Answers  


A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).

9 Answers  


If relative y axis vibration sensor is by passed, and relative x axis and absolute sensor is left working. how much monitoring i would have risked?

0 Answers  


hiii.... can any one provide me previous years question paper of hindustan petroleum for instrumentation engineering???

0 Answers  


in control valve is constructed as per API 6D or API 6A, then which standard is used for fire testing of valve?.

1 Answers  


HOW TO CALCULATE WAKE FREQUENCY FOR THERMOWELL???WITH OUT SOFTWARE..

1 Answers  


Generally in which location ( JB or IO card or DCS) the thermocouple compensation is done.Also where they measure the atmosphere temp ( for compensation) in JB OR DCS panel? How they compensating that atmosphere temp? is any circuit for that ( like in rtd wheatstone bridge)?

3 Answers  


If we interchange HP and LP tapping in drum level measurement and reverse LRV & URV correspondingly.What is the difference between the normal tapping(HP,LP) and reversed tapping(LP,HP)?

2 Answers  


What is the purpose of the analyzer in petrochemical plant?

0 Answers   ENI, Lakshmi Machine Works,


i m passed my engineering in 2010 in instrumentation and control engineering. my question is can i apply for software jobs or vacancies.??????????? plz give me answer soonnn......

2 Answers  


I have 0.75mm sq multicore cable (IS type) , can use instead of same type but 1.5 sq mm cable ? Note : The distance is around about 150 meter.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)