How to check vortex flow meter is in good condition while
we do not having calibration setup?
Answers were Sorted based on User's Feedback
Answer / krishna reddy
Let me know first which make you have.
Instrument have min and max ranges on its name plate.
So wiht multimeter you can check 4-20ma of flow meter.It
must be 4 ma if flow is zero and 20ma if flow is max range.
supose your flow mete got 100L/hr.
for 4ma flow should be 0 L/hr
8ma - 25L/hr
12ma - 50L/hr
16ma - 75L/hr
20ma - 100L/hr
Like this you can check.
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / amit
U can do the cold test by checking the sensor.It has piezo
sensors in symetrical manner. U can check both piezo
sensor by checking the capacitance. If capacitance is
accordance with size means sensor is OK. same way u can
check temp and pressure sensor(by checking the resistance)
if it has.This way u can check the healthiness of the
sensor. If u want to check the response of sensor, u can
give little vibration to the sensor by hammering on it and
check the response on transmitter. U cannot directly check
the calibration for flow on field itself.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / tuhin
@soumil: no hp and lp side exist in vortex flowmeter. Vortex
principle is different.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / saumil
In this meter hp or lp any one side we isolate line valve and check zero if it is ok then meter is ok
Is This Answer Correct ? | 1 Yes | 3 No |
During the design and engineering of a process plant, a good designer should plan for ____________, ___________ and ____________ aspects of the plant
how to convert digital signal to analog signal in plc
Drum level tx with GP4 with zero elevation:7300mmh20 on HP and 8050mmh2o on LP as range but on commissioning the tx readiing is max,Why this reading?
what is hart communicater? can u give brief explanation about this issue?
what step is taken for ESD ( emergency shut down) in DCS REPLY to hashimka20009@gmail.com
0 Answers Bosch, Eskom, Sabic,
why we are using MARSHALLING PANEL? what is the role?
why need 3 element system in power plant? if it is not there then what l happen?
we have level transmitter for h2s04 storage tank capacity 10k ,always there are failure of transmitter due to failure of magnetic floats ,please come up with solutions at the earliest.
what is the difference between sensor and tranducers?
i feel sq. pipe is better than round pipe pls give comment for this. advance thanks for reply
what is radar type level transmitters and its basic principle and how to calibrate it
how to calculate signal cable sizing? and multipair cable sizing??explain in brief?