Answer / tuhin
an autotransformer will be smaller than an equivalent
conventional transformer. The reason is an autotransformer
essentially has one winding on a core, with one tap
including the whole winding, and another tap including only
part of the winding. In a conventional transformer, power
is transferred from one winding to the other by induction.
In an auto, some is by conduction, and some is by induction.
Here's an example comparison:
Say we have a 10MVA 100kV/50kV 3 winding auto transformer.
There are two parts of the winding - the series winding
(the section of winding between the 100kV connection and
50kV connection), and the common winding (the section of
winding between the 50kV connection to the neutral). If
powered at 10MVA (full load), there will be:
10M / (100k * sqrt(3)) = 57.7 Amps flowing into the
primary, and
10M / (50k * sqrt(3)) = 115.5 amps flowing out of the
secondary
So, 57.7A flow into the primary, down through the series
winding and out the secondary. At the same time 57.7A flow
up from the neutral through the common winding and out the
secondary, resulting in a total secondary current of (57.7
+ 57.7) = 115.5 (sorry, rounding is making my math look
wrong!).
Thus, the series winding is handling a total of:
(100k - 50k)* 57.7A*sqrt(3) = 5MVA, and the common winding
is handling a total of:
(50k - 0) *57.7A*sqrt(3) = 5MVA
So the series and common windings only have to be made to
handle 1/2 the total load(for this example - it is 1/2
because the primary / secondary voltage is 2/1). In a
conventional transformer, each winding carries the full
load (10MVA), because it operates on induction (no
conduction).
If the votlage ratio between primary and secondary is too
high, there is no real net savings in size (and thus cost),
so a conventional transformer is often used. The cutoff
point is around 4.
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / sivachandran
Auto transformer is a single winding transformer. In auto
transformer single winding is works both primary and secondary
| Is This Answer Correct ? | 4 Yes | 6 No |
We are getting supply at33kvand it stepdown to 11kv.So Our requirement is 11kv voltage.why we draw 33kv from the grid instead of 11kv?
what is looping circuit in electrical lighting circuits?
If u have Powergrid model question papers Please send to below mail ID rajutheprince@gmail.com
How the flights will be fly be fly without ground connection under raining with thunder lighting?
what are the industrail measures to overcome ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system? plz reply
If two hack saw blades, seperated by 1mm thick paper,are connected across 230volts, and immersed in water,then they start getting heat. This is fact,i dont know how they get heated.Blades are not directly connected together. Please if anybody knows the fact ,revert back to me
what is the difference between dropout fuse and horn gap fuse. how to choose between them
What is neutral and how to produced
How relay works, reverse relay, master relay, os relay, earth fault relay and what is its setting point
what is the preventive @ predective maintenance
what is closing resistor in circuit breaker? why it used?
what happens if we earth negative electrode of an rectifier transformer used in ESP. In which normaly positive is earthd from inside the xmer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)