why we are using auto transformer in sub station mostly???
Answers were Sorted based on User's Feedback
Answer / tuhin
an autotransformer will be smaller than an equivalent
conventional transformer. The reason is an autotransformer
essentially has one winding on a core, with one tap
including the whole winding, and another tap including only
part of the winding. In a conventional transformer, power
is transferred from one winding to the other by induction.
In an auto, some is by conduction, and some is by induction.
Here's an example comparison:
Say we have a 10MVA 100kV/50kV 3 winding auto transformer.
There are two parts of the winding - the series winding
(the section of winding between the 100kV connection and
50kV connection), and the common winding (the section of
winding between the 50kV connection to the neutral). If
powered at 10MVA (full load), there will be:
10M / (100k * sqrt(3)) = 57.7 Amps flowing into the
primary, and
10M / (50k * sqrt(3)) = 115.5 amps flowing out of the
secondary
So, 57.7A flow into the primary, down through the series
winding and out the secondary. At the same time 57.7A flow
up from the neutral through the common winding and out the
secondary, resulting in a total secondary current of (57.7
+ 57.7) = 115.5 (sorry, rounding is making my math look
wrong!).
Thus, the series winding is handling a total of:
(100k - 50k)* 57.7A*sqrt(3) = 5MVA, and the common winding
is handling a total of:
(50k - 0) *57.7A*sqrt(3) = 5MVA
So the series and common windings only have to be made to
handle 1/2 the total load(for this example - it is 1/2
because the primary / secondary voltage is 2/1). In a
conventional transformer, each winding carries the full
load (10MVA), because it operates on induction (no
conduction).
If the votlage ratio between primary and secondary is too
high, there is no real net savings in size (and thus cost),
so a conventional transformer is often used. The cutoff
point is around 4.
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / sivachandran
Auto transformer is a single winding transformer. In auto
transformer single winding is works both primary and secondary
| Is This Answer Correct ? | 4 Yes | 6 No |
What is the maximum number of swithes that can be connected in series up to down stream point in an LV Distribution system?
Thumb rule of cable size(rm>30 rm)X multiplying factor=ampere
0 Answers Kazi Farms, SKI Carbon Black,
if the synchronizing b/w generator and busbar not complete and we close the out going circuit breaker of generator then what happen ?
How much ampere rating on LT side of distribution transformer and also on HT side of 200KVA transformer
Why does the adjacent zone of protection overlap?
sir iam from electrical and electronics branch ,can i appear for the hpcl offline requirtment? if yes please mail me on vikram_raju25@yahoo.co.in
what is meant by LCR meter? where its useful ?
What is various types of electrical formula?
I have a shop heater with a 1/3 hp capacitor start, induction motor driving the fan. Intermittently, the fan motor speeds up significantly for several seconds (15-60 sec) then slows to normal operating speed. The manufacturer suggested changing the capacitor which made no sense, but I did it to no avail. Could this possibly be caused by the centrifugal switch intermittently reconnecting the start winding?
why are the a.c.series motors preferred for electric traction
What are the various types of BUSBAR Schemes? explain each
is power factor correction related with vector group of transformer i.e:Dyn11?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)