Will it be OK to connect a 5MVA 33/6.6kV Ynd11 Transformer
to a Star connected Motor. Or on other words connecting a
Delta to a Star.
I have another 30MVA 33/11 Dyn11 and would it be practical
to convert it to Dd0 consequently converting the Voltage
Ratio to 33/6.35kV Dd0.
yes. what is the capacity of motor?
In your case , grid voltage is 33kv, Yn connected.Hence
power transformer has neutral connection brought
out.Neutral CT is installed to detect the ground faults.
secondary of 5MVA tranformer is 6.6kv,
This is Feeder bus voltage.6.6kv Feeder bus feeds Motor (
star connected). and Feeder bus is not interconnected to
another source. It is independent.This 6.6kv rotates at 30
lagging to primary3kv system.
Motor must be use inverse & instantaneous time
overcurrent and earth fault ( CDG61+cdg12) or equivalent
manufacturer protection
we use delt to star as weelas star 6.6motor.
No problems experienced.
In the othercase to change a 30MVA,33/6.35KV IS
REDESIGN/MANUFATURING. iT IS EXPENSIVE.No use at all and
advantage. You should change 6.6kv sw.gr also.
Is This Answer Correct ? | 1 Yes | 0 No |
what is laser diodes?
State the difference between Three winding transformers and Two winding transformers ? where its used?
difference between circuit breaker and switchgear?
Can anybody tell me how to calculate(formula) earth flat size(for copper and aluminium).
Some times to change of DOR of a motor, interchange of R & B is not effected and RYB take same current, but interchange of R&Y is effected ie change the DOR. My doubt is what is the problem in motor and how it is happen.
what is ATS?and its function or operation in power system with its layout.
advantage of motor design on higher power factor . normally motors are designed for .8 power factor. what is advantage of designing at .88 power factor
i have 500 amp inductive load of motors ,,,pleas tell me how can i calculate for capacitor bank for improving my power factor to 99 .....calcullations for capacitor bank,,,,
how we could know that generator running anti clockwise with seeing the rotating direction of prime mover or engine
In wat way the power compensation takes place when a statcom is connected in a transmission line
what are the standard values for resistances(Megger testing) between L&N, L&E and N&E (L=Live,N=Neutral, E=Earth)?
what are the causes for strip heater failure ?