I want to know what must the CT ratio be on a load of 300A
is a 3PH nutral to earh installation?
Answers were Sorted based on User's Feedback
Load current is 300A. The equipment shall withstand the
starting current -which is around -5-8xIn.It is preferable
to select 1ooo-1200A/1A OR 5A.
WE ADOPT THIS THUMB RULE for our protection setting& co-
ordination.
Is This Answer Correct ? | 0 Yes | 0 No |
The neutral is a point in power transformer or in motor
connection where all phases are connected.In this point
voltage is zero. when you connect thisoint to earth, the
fault current or capacitance circulating current flows to
earth.
when a fault occurs , current is high.Therefore,CT ratio
should be 1000-1200/5 or 1A.
It is usually upto designer or protection device supplier.
Is This Answer Correct ? | 0 Yes | 1 No |
What is chopper
how to calculate busbar capacity for 1000Kva transformer having22/.433V
2 Answers Electrical Tech, L&T,
What is warm / cold start of HT motors. How many warm start & cold start are possible in a day?
What are the maximum and minimum ratings of MCB,MCCB,ACB,OCB,VCB and SF6 breakers?
2 Answers ABB, SK E&C, Sodexo,
What happens with squirrel induction machines if the ends of rotor conductors are kept open? Explain
hi if anybody got model questions for cpcl Grade'A' electrical engineer position.send it to my mail please krishkumar22@gmail.com
What is power factor ?What are the benefits of improved power factor & how. Please explain with examples.?
Electromotive force is provided by:(a) Resistance’s(b) A conducting path(c) An electric current(d) An electrical supply source
how do u get less voltage in star connection
What is the principal of motor?
why the voltage and current in a long transmission line are called travelling wave?
WHY WE NEED AUTO TRANSFORMER,WHERE WE CAN USE?