Part -I:
400Ah Battery means the battery can supply a DC load of 400
Amps for a duration of 1 Hour until the battery gets fully
discharged. so if you are using the battery to supply the
above mentioned load of 20 Amps the battery can work for
400/20 = 20 Hours. provided the 20Amps is a Direct load
connected to the Battery. if you use the battery for a
inverter or UPS to suplly an AC load of 20 Amps. then the
duration is different.
Part - II:
For charging any battery we have to provide a voltage that
is slightly (5% - 10%) higher than the Battery terminal
voltage. The duration of charging can be known by the same
process as above. A 400Ah gets charged in 1 Hour provided
the charging source is capable of supplying 400 Amps to the
Battery. But normally the current of the charging source
will be limited to a lesser finite value. so if you can
know the maximum load the source can supply you can easily
calculate the duration required for the battery to get
fully charged.
| Is This Answer Correct ? | 27 Yes | 5 No |
Answer / dharmendra kumar gautam
20hours for fully charged of 400ah battery bank
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / suyog
if we connected many cells (24) of 200Ah then how i calculate its back up for 10Amp load
| Is This Answer Correct ? | 3 Yes | 0 No |
Why shunt Generator is not recommended to start at ON LOAD condition???
Explain why the Voltage drop will happen in 3 Phase line?
What is slip in an induction motor?
How much weight an electrical engine can pull??
Why DG self motor winding burnt out?
Can the same motor be operated in both direction ?
Dear all, I'm manikandan I have done by DIPLOMA EEE from 2011 , I have 5 years of experience from Power plant instrumentation field , which one field is give long life & which one field is best ,I confused a lot and also I'm studying AMIE, can I choose which department from Section B examination? pls tell me
Why iron core transformers not used in high frequency applications ?
working function importance of mdc meter
Single line diagram for dbb (double bus bar)system.
technically, what is the reason behind starting the motor star the delta connection .. and what other ways to do this rather than using " star-delta transformer"
Is it acceptable of installing an earth pit in planters area where bare copper cable, earth rod and connection are susceptible to corrosion due to water?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)