How to calculate battery back up time for a 400 AH battery
bank installed in telecom shelter for a load of 20 Amps and
time taken to fully charge this battery bank?
Answers were Sorted based on User's Feedback
Part -I:
400Ah Battery means the battery can supply a DC load of 400
Amps for a duration of 1 Hour until the battery gets fully
discharged. so if you are using the battery to supply the
above mentioned load of 20 Amps the battery can work for
400/20 = 20 Hours. provided the 20Amps is a Direct load
connected to the Battery. if you use the battery for a
inverter or UPS to suplly an AC load of 20 Amps. then the
duration is different.
Part - II:
For charging any battery we have to provide a voltage that
is slightly (5% - 10%) higher than the Battery terminal
voltage. The duration of charging can be known by the same
process as above. A 400Ah gets charged in 1 Hour provided
the charging source is capable of supplying 400 Amps to the
Battery. But normally the current of the charging source
will be limited to a lesser finite value. so if you can
know the maximum load the source can supply you can easily
calculate the duration required for the battery to get
fully charged.
Is This Answer Correct ? | 27 Yes | 5 No |
Answer / dharmendra kumar gautam
20hours for fully charged of 400ah battery bank
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / suyog
if we connected many cells (24) of 200Ah then how i calculate its back up for 10Amp load
Is This Answer Correct ? | 3 Yes | 0 No |
To attain a powerfactor more than .95, how much kvr should we use for 100 HP of current
4 Answers Bhel, Scooters India,
What is the source of dependent source ?
pls tel me the electric train traction motors name plate details like rpm,torue,voltage,amps,watts..ect..
Why (In India) we preferably go for +-30 deg connection of transformer? what are the advantages in this connection?
why power factor is only cosine angle not sine angle?
What is floating earthing?
What is the effect on Power factor and capacitor when your company load is more than 70 % of welding transformer
1-What is the difference between absorption factor and polarization factor in insulation resistance test in transformers? and why we inject until ten minutes to get polarization factor?
Please give me a erda placement paper
Which Motor used in Fan's Motor ?
3 Answers Matsui Technologies,
what is the full form of FRL (3/20,7/20 EARTH WIRE)..????
3 Answers Aster, Divis Laboratories, FRL, Gasco,
what is the formula to calculate the fuel consumption of a diesel generator at different diferent load.
4 Answers Aegis, Network Clothing Company,