What is maximum permissible length of cable from transformer
(33kV/0.433kV) HT side to HT panel which contain VCB? In
which standard i shall get this information.
Answers were Sorted based on User's Feedback
Answer / satyajitt_1983
Before calculating the Cable length we have to decided the
cable size which is depend upon the terminal size of
Transformer & HT panel. After selection of cable size & no
of run we have to calculate the voltage drop which should
be within the limit of the specified project.
| Is This Answer Correct ? | 5 Yes | 0 No |
this is a practical problem.
Generally , Station auxiliary or Unit auxiliary
transformers are located very near to load consummer PCC/mcc
building.
High voltage current is less and Low voltage current is
very high,say 1250kva-33/0.42kv,21/1800A,
5MVA,33/0.42KV,87A/7210A. therefore, the distance between
33kv MV SW.GR FEEDER to your transformer location could be
500-1000m as per voltage drop calculation.we have the
system around this distance.
the advatage is LOw voltage from power transformer to PCC
SW.GR IS BUS DUCT. Huge low voltage power cable are totally
eliminated. Maintenanve free. electrical engineering hand
book.siemens ,abb
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pravin
if a long cable is connected what will happen to charging
current & surges that may affect transformer winding. Also
the protection given to transformer is overcurrent & earth
fault that may not work properly, it may mal operate. I am
surching for any standrad that could specificaly mention
this matter.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / pravin
Actualy this problem is occuring in solar power plant. we
need some standard no to justify.
| Is This Answer Correct ? | 1 Yes | 1 No |
That would be subject to your local electrical code. If the
run of cable is outside, usually no limit. Inside there is
a limit to the length. There are provisions if it is
underground such as depth ,conduit type, concrete encased,
maybe others per your code.
Respond to this post.
| Is This Answer Correct ? | 2 Yes | 3 No |
Buchholz relay is used ………. a) protection T/F b) oil T/F c) Air core T/F
8 Answers Engineers India Limited,
application s to shunt coil
In a three-phase full converter, output voltage pulsates at frequency of a. f b. 2f c. 3f d. 6f
WHAT IS MEANT BY SYNCHRONISING IN GENSETS
in short circuit. test of a transformer 5 to 10% ofvrated voltage is used why??? if we use rated voltafe then what will be?
how many types in CT & define it ?
If I need to purchase a step-down transformer (from three phase 33kV 50Hz to 400/230V), what additional information do I need from the main supply power line?
what is the full form of KVAR
single phase brower fan with control starter. *problem is when operate it.It will be trip.
What is the operating range of voltage and current in grid supply in India?
Which UPS (inverter) is better and why ? 12 V inverter and 24 V (two 12 V batteries in series) inverter which is better ......... which has the longer backup which has the greater charging time which has the greater discharging time thank you
WHAT WILL HAPPEN IF WE START A MOTOR WITH STAR & IT IS RUNNING WITH STAR CONNECTION INSTEAD OF DELTA
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)