Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is maximum permissible length of cable from transformer
(33kV/0.433kV) HT side to HT panel which contain VCB? In
which standard i shall get this information.

Answers were Sorted based on User's Feedback



What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / satyajitt_1983

Before calculating the Cable length we have to decided the
cable size which is depend upon the terminal size of
Transformer & HT panel. After selection of cable size & no
of run we have to calculate the voltage drop which should
be within the limit of the specified project.

Is This Answer Correct ?    5 Yes 0 No

What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / a.p.nanjappa

this is a practical problem.
Generally , Station auxiliary or Unit auxiliary
transformers are located very near to load consummer PCC/mcc
building.
High voltage current is less and Low voltage current is
very high,say 1250kva-33/0.42kv,21/1800A,
5MVA,33/0.42KV,87A/7210A. therefore, the distance between
33kv MV SW.GR FEEDER to your transformer location could be
500-1000m as per voltage drop calculation.we have the
system around this distance.
the advatage is LOw voltage from power transformer to PCC
SW.GR IS BUS DUCT. Huge low voltage power cable are totally
eliminated. Maintenanve free. electrical engineering hand
book.siemens ,abb

Is This Answer Correct ?    3 Yes 0 No

What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / pravin0021

Electrical Enginnering

Is This Answer Correct ?    3 Yes 2 No

What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / pravin

if a long cable is connected what will happen to charging
current & surges that may affect transformer winding. Also
the protection given to transformer is overcurrent & earth
fault that may not work properly, it may mal operate. I am
surching for any standrad that could specificaly mention
this matter.

Is This Answer Correct ?    2 Yes 1 No

What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / pravin

Actualy this problem is occuring in solar power plant. we
need some standard no to justify.

Is This Answer Correct ?    1 Yes 1 No

What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel whi..

Answer / wareagle

That would be subject to your local electrical code. If the
run of cable is outside, usually no limit. Inside there is
a limit to the length. There are provisions if it is
underground such as depth ,conduit type, concrete encased,
maybe others per your code.
Respond to this post.

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

why d.c produces corrosion

0 Answers  


what is the earth resistance ?

5 Answers   Bhel, Cummins,


Can I use less voltage cable for neutral, since the voltage of return path is zero ideally?

3 Answers   Vijai Electricals,


What is the function of isolater

4 Answers   Getco, Gland Pharma,


for star delta connection,,why the contactor star not burn,when red,yellow and blue cable is looping.

2 Answers   Mahindra Water Utilities,


Why we make earth connection with Transformer Body and What will be the minimum size of copper wire as per code with respect to KVA rating of Transformer?

0 Answers  


in case of transformer the power factor is depend on input or the output

1 Answers  


what is iron loss?

4 Answers   RRB,


what are eddy currents

2 Answers  


What current flows in the transformer primary when its secondary is open?

0 Answers  


How to select a cable size according to load

1 Answers   Red Bull,


which type motor r use in the celling fan.....

6 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)