What is maximum permissible length of cable from transformer
(33kV/0.433kV) HT side to HT panel which contain VCB? In
which standard i shall get this information.
Answers were Sorted based on User's Feedback
Answer / satyajitt_1983
Before calculating the Cable length we have to decided the
cable size which is depend upon the terminal size of
Transformer & HT panel. After selection of cable size & no
of run we have to calculate the voltage drop which should
be within the limit of the specified project.
| Is This Answer Correct ? | 5 Yes | 0 No |
this is a practical problem.
Generally , Station auxiliary or Unit auxiliary
transformers are located very near to load consummer PCC/mcc
building.
High voltage current is less and Low voltage current is
very high,say 1250kva-33/0.42kv,21/1800A,
5MVA,33/0.42KV,87A/7210A. therefore, the distance between
33kv MV SW.GR FEEDER to your transformer location could be
500-1000m as per voltage drop calculation.we have the
system around this distance.
the advatage is LOw voltage from power transformer to PCC
SW.GR IS BUS DUCT. Huge low voltage power cable are totally
eliminated. Maintenanve free. electrical engineering hand
book.siemens ,abb
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pravin
if a long cable is connected what will happen to charging
current & surges that may affect transformer winding. Also
the protection given to transformer is overcurrent & earth
fault that may not work properly, it may mal operate. I am
surching for any standrad that could specificaly mention
this matter.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / pravin
Actualy this problem is occuring in solar power plant. we
need some standard no to justify.
| Is This Answer Correct ? | 1 Yes | 1 No |
That would be subject to your local electrical code. If the
run of cable is outside, usually no limit. Inside there is
a limit to the length. There are provisions if it is
underground such as depth ,conduit type, concrete encased,
maybe others per your code.
Respond to this post.
| Is This Answer Correct ? | 2 Yes | 3 No |
in DG synchronization system can i short R,Y,B- phase(DG-1) to R,Y,B Phase (DG-2), HOW IT WORK . WHAY WE NEED TO SYNCHRONIZATION.
what is function and advantage of double delta winding in induction generator?
I am shobana from Chennai. I am having my personal interview on 19th Dec at Chennai.kindly mail me the questions to mail id shobana.shanthi@gmail.com
why we take movement of rotor always in counter-clockwise direction in 3-phase induction motors?
how we do Vector group ,magnetic balance and tap changer test in Transformer?
At what point crngo works like as crgo
hi pot test principal
can we run three phase motor by single phase? and what happens if we do this
how to reduce humming noise in transformer?
i want prepare power grid exam what are book we want refer for electrical ?
One Township having 850 house and each house load is 2.2KW single phase & 5HP 3 Phase motors of 10 Nos .Who can calculate 11 KV transformer capacity .dilip_bhasker@yahoo.co.in
How to derive detailed design of Suitable bus Bar for 100A for 6.6KV?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)