What is maximum permissible length of cable from transformer
(33kV/0.433kV) HT side to HT panel which contain VCB? In
which standard i shall get this information.
Answers were Sorted based on User's Feedback
Answer / satyajitt_1983
Before calculating the Cable length we have to decided the
cable size which is depend upon the terminal size of
Transformer & HT panel. After selection of cable size & no
of run we have to calculate the voltage drop which should
be within the limit of the specified project.
Is This Answer Correct ? | 5 Yes | 0 No |
this is a practical problem.
Generally , Station auxiliary or Unit auxiliary
transformers are located very near to load consummer PCC/mcc
building.
High voltage current is less and Low voltage current is
very high,say 1250kva-33/0.42kv,21/1800A,
5MVA,33/0.42KV,87A/7210A. therefore, the distance between
33kv MV SW.GR FEEDER to your transformer location could be
500-1000m as per voltage drop calculation.we have the
system around this distance.
the advatage is LOw voltage from power transformer to PCC
SW.GR IS BUS DUCT. Huge low voltage power cable are totally
eliminated. Maintenanve free. electrical engineering hand
book.siemens ,abb
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pravin
if a long cable is connected what will happen to charging
current & surges that may affect transformer winding. Also
the protection given to transformer is overcurrent & earth
fault that may not work properly, it may mal operate. I am
surching for any standrad that could specificaly mention
this matter.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / pravin
Actualy this problem is occuring in solar power plant. we
need some standard no to justify.
Is This Answer Correct ? | 1 Yes | 1 No |
That would be subject to your local electrical code. If the
run of cable is outside, usually no limit. Inside there is
a limit to the length. There are provisions if it is
underground such as depth ,conduit type, concrete encased,
maybe others per your code.
Respond to this post.
Is This Answer Correct ? | 2 Yes | 3 No |
can any one provide me a connection wiring diagram for a DG set control panel along with BOM?
If only R Phase is connected in 2 pole elcb, n is not connected than it will work or not in ground fault.
raleigh method
why the capacitors works on ac only
Which type of motor is used in trains, what is the rating of supply used explain working principal?
in CNC reference how to take? what kind of input give to the servo amplifier?
sir, in a industry present pf is 0.54 pf 25hp power is there its want improve 0.9 pf. which suitable capacity capacitor is suitable please inform me.
Is there any problem if i connect APFC panel in generator circuit
why transformer do not rotate?
Why voltge arev transformed in to 132KV/66/KV/33KV like that
slor cell made?