What is the power ratio between power in Star and Delta
circuit?
Answers were Sorted based on User's Feedback
Answer / baswaraj
The power ratio between Star to Delta is 1:3
Here is the Explanation:
Let?s suppose Vs be the supply voltage per phase.
So the line voltage of the supply will be ?3Vs.
Now assume any type of load; for simplicity assume it a
only resistive load.
And let it be ?R? per phase.
For Delta connected load:
Calculation for per phase power; PD= I2R
Where I ? load current (per phase)
And,
I = ?3Vs/R {as line voltage of the supply is directly
applied to the phase of the delta load}
So,
Pd = (?3Vs/R )2R = 3Vs2/R watts per phase.
For 3 phases:
P3D = 3Pd = 3*3Vs2/R = 9Vs2/R watts.
Now for Star connected load:
PS = I2R = (Vs/R)2R = Vs2/R watts
For 3 phases: P3S = 3PS = 3 Vs2/R watts
Conclusion:
P3S / P3D = 3Vs2/R / 9Vs2/R = 1/.
Is This Answer Correct ? | 26 Yes | 58 No |
Can we provide 3phase wire in conduit for room?
What is the difference between KW & KVA ?
what is the diffrence between earth and neutral.
How vaccum is formed to create a vaccum interrupter or anything related with vaccum?
What is d role of reactive power in power system??How it produce & consume?
why earth fault current is always less than the o/c
which of the folowing has negative temperature coefficient of resistance? a. mercury b. copper c. lead d. carbon
Hi How can you start-up the 40w tube lite with 230v AC/DC without using any choke/Coil.
why lightning arrestor are made in two stack of insulator but why not cvt
How voltage step down is done?
How many size of cable required for a 300m long and 30kw inductive lode
Dear all,recently in our plant we installed a conveyor for this the motor ratings are 5 hp and Amps 7.39.Due to on urgent starting of conveyor we fix the DOL starter with range of 9-15 amps.give me suggestion regarding on this issue