What is the power ratio between power in Star and Delta circuit?..

Answer / baswaraj

The power ratio between Star to Delta is 1:3

Here is the Explanation:

Let?s suppose Vs be the supply voltage per phase.

So the line voltage of the supply will be ?3Vs.

Now assume any type of load; for simplicity assume it a
only resistive load.

And let it be ?R? per phase.



For Delta connected load:



Calculation for per phase power; PD= I2R



Where I ? load current (per phase)

And,

I = ?3Vs/R {as line voltage of the supply is directly
applied to the phase of the delta load}

So,

Pd = (?3Vs/R )2R = 3Vs2/R watts per phase.

For 3 phases:

P3D = 3Pd = 3*3Vs2/R = 9Vs2/R watts.



Now for Star connected load:



PS = I2R = (Vs/R)2R = Vs2/R watts

For 3 phases: P3S = 3PS = 3 Vs2/R watts



Conclusion:

P3S / P3D = 3Vs2/R / 9Vs2/R = 1/.

Is This Answer Correct ?    26 Yes 58 No

Post New Answer

More Electrical Engineering Interview Questions

Can we provide 3phase wire in conduit for room?

1 Answers  


What is the difference between KW & KVA ?

9 Answers  


what is the diffrence between earth and neutral.

1 Answers  


How vaccum is formed to create a vaccum interrupter or anything related with vaccum?

6 Answers  


What is d role of reactive power in power system??How it produce & consume?

5 Answers   ABB,






why earth fault current is always less than the o/c

2 Answers  


which of the folowing has negative temperature coefficient of resistance? a. mercury b. copper c. lead d. carbon

2 Answers  


Hi How can you start-up the 40w tube lite with 230v AC/DC without using any choke/Coil.

5 Answers  


why lightning arrestor are made in two stack of insulator but why not cvt

0 Answers  


How voltage step down is done?

3 Answers   IOCL,


How many size of cable required for a 300m long and 30kw inductive lode

0 Answers  


Dear all,recently in our plant we installed a conveyor for this the motor ratings are 5 hp and Amps 7.39.Due to on urgent starting of conveyor we fix the DOL starter with range of 9-15 amps.give me suggestion regarding on this issue

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)