a 650 KVA diesel generator is 1500 rpm, voltage is 415V n full load amps is 805 something,when are applied load more than 400 amps it's voltage is dropping, what is the reasons...?
Answers were Sorted based on User's Feedback
Answer / sanjay
There can be one of the following reason for the problem :
1.The AVR may be faulty.
2.The conductor is of lesser current rating.
3.Loose connection/faulty cable termination
4.Load is quiet far off from generator.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / dharmans
1.mainly in AVR RRA diodes problem or lose termination.
Is This Answer Correct ? | 3 Yes | 0 No |
iT SEEMS THE EXCITATION SYSTEM IS NOT TUNED PROPERLY.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / satya dev
There is a lot of reasons to droping thevoltage during the
load.
Electrical reason - 1. Excitation voltage is not build up
to the requiered limit.
2.Fuel pump actuator is not working properly.its required a
certain DC voltage for certain load.
Mechanical Reason- If the DG set is more than two cylinders
may be one piston is not working properly, may be push rod
of the piston got broken.
Is This Answer Correct ? | 0 Yes | 0 No |
electical engg basic question
What is the size of cable to be used for a Space Heater in UPS 160KVA of carrying 10 Amps current with 240 V ,1 Phase?
Why synchronous motor is used in power factor improvement,dc series in lift
What are the tests to be taken on a transformer and generator?
how we calculate the withstansing current capacity of wires&cables?
Define motor & pump?
what is the working of air compressor.
how to interlock 3 nos MCCBs using under voltage coil. please provide me circuit diagram?
Does the electricity supply authority send its customers power (kW) or voltape (V)? Asked by Ivan Muliro
AVR
What do u understand voltage reg. of an alternator?
IN OLTC we observed "OUT OF STEP" Alarm, we have two different transformer, when both are in parallel this type of alarm observed. what's the meaning of this alarm and why it occurs???