a 650 KVA diesel generator is 1500 rpm, voltage is 415V n full load amps is 805 something,when are applied load more than 400 amps it's voltage is dropping, what is the reasons...?
Answers were Sorted based on User's Feedback
Answer / sanjay
There can be one of the following reason for the problem :
1.The AVR may be faulty.
2.The conductor is of lesser current rating.
3.Loose connection/faulty cable termination
4.Load is quiet far off from generator.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / dharmans
1.mainly in AVR RRA diodes problem or lose termination.
| Is This Answer Correct ? | 3 Yes | 0 No |
iT SEEMS THE EXCITATION SYSTEM IS NOT TUNED PROPERLY.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / satya dev
There is a lot of reasons to droping thevoltage during the
load.
Electrical reason - 1. Excitation voltage is not build up
to the requiered limit.
2.Fuel pump actuator is not working properly.its required a
certain DC voltage for certain load.
Mechanical Reason- If the DG set is more than two cylinders
may be one piston is not working properly, may be push rod
of the piston got broken.
| Is This Answer Correct ? | 0 Yes | 0 No |
Can u tell me the name of books of transformer testing?
sometime battery charged and then automatically charged when rectifier ON conition, is there any chances please clarify the same.
Explain Continuous and Discrete signals?
i have need all detail above basic transformer question..
Dear sir my name Ankit i m Diploma holder present working in Welspun Corp ltd Anjar as Asst.engg (salary 14400/month ctc) i Would like to change my company also i have selected in ford India pvt ltd Sanand as trainee Tech with salary 12000/month so please suggest me for changing my job hope for *ve response
In any plant or substation main incommer voltage RY - 415 V,YB - 400 V, BR - 387 V(in commer feed from transformer 11 Kv /0.415 KV) why found voltage differance in each phase? plant have not self power plant it is depend on outsource grid
how do you select the ct/pt rating in substation
1 Answers Apollo, Shreem Electric Ltd, Tata Motors,
what is role of mpu in dg
how much speed will trawiling current
What is the method to calculate the capacitor bank rating for say 50 KW load and how do we connect each capacitor to busbar??
in most industies hormonics present up to some level. what is limit ? and there effect?
why d.c. supply is given to the primary side of generator?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)