What is the method to calculate the capacitor bank rating
for say 50 KW load and how do we connect each capacitor to
busbar??
Answers were Sorted based on User's Feedback
Answer / amrinder
50 KW is 68 hp ,that means we have to connect three 22.5
KVAR capacitors in delta..?? Please Justify
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / vijay kumar
Actually motors are designed at 0.8pf.
50kw load means 50/0.8 kva i.e to 62.5 kva
we know that kvar=kva*sin(angle b/w V & I)
To take Power factor to Unity we need Kvar=62.5*0.6
=37.5 kvar
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / santoshvarma
Before connecting a capacitor bank we have to know for what
purpose we are connecting, if the load having power factor
of 0.8 and if you want to increase the power factor to 0.95,
for that you need to install capacitor bank. The rating of
the capacitor bank can be calculated as follows
Required KVAR rating of capacitor bank = KW(of
load)*(tan(cosinver 0.8)-tan(cosinve0.95)
By this way you will get the kvar rating of capacitor bank.
The capacitor is always connected in parallel to load bus.
| Is This Answer Correct ? | 2 Yes | 2 No |
In case of power/distribution transformer what is percent impedence?
Wheather there exist any dc transformer
can HT cable or HT bare conductor used for LT line? is yes what would be the current rating?
what work will do diffrential realay DG set
0 Answers IG Petrochemicals Ltd,
dg started in plc mode and load taken later one battery terminal connection will be disconnected by loose connection what will happen for dg and shall we connect battery terminals while dg in load time?
what is the difference between surge arrestor and lightning arrestor ?
induction 3 phase motor terminal connection
will a bulb glow connected to two phases of a delta connection?
hi!!! i have a question that how the thermal test in winding temprature test is taken can anyone explain me in detail??? i will b very thankful!!!!
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
Why the frequency of a system is changed if the load changes?
Dg daily a check duration
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)