in our 6.6kv motor feeder[it is having two sources from
Bus A&B] earth fault relay is acting, we checked CBCT
connection and cable meggerd values found very good still
earth fault acting during first two are three start after
that it will hold. please clarify what was the reason. if
same motor is starting from other Bus-A it will start.
WHAT IS THE TYPE OF 6.6KV SW.GR. hOW OLD IS THIS?
tHE EARTH FAULT RELAYS ARE VERY SENSITIVE. INSULATION
RESISTANCE OR MEGGER CAN NOT MEASURE.
CARRY OUT HV CAPACITANCE MEASUREMENT OF MOTOR,CABLE FEEDER.
AND hIGH POT TEST.
MEASURE THE TANGENT DELTA FROM DC HIGH POT.
IF MIN OIL CIRCUIT BREAKER,TEST THE OIL AND REPLACE.
WE ALSO EXPERIENCED THIS DUE TO BURNED CEREMIC/BAKELITE
PARTITION PLATES OF 6.6KV SW.GR
| Is This Answer Correct ? | 0 Yes | 1 No |
Explain Power factor in simple words
i asked a funny question in Electrical ohms law V=IR in const temp voltage is directly proportional to current Power p=VI cos@ in that formula Voltage is indirectly proportional to current Try to give me the fact what is happening in Electrical.. contact Thanigai_1984@yahoo.co.in
what is the difference between E.L.C.B & R.C.C.B?
how we calculate the knee point of a protection and metering CT and what is the testing procedure.
What is the use of insulation tester and how it is to be used.
What are the temperature elements?
WTA used cb?
from which formula we select a capacitor rating?
In a 3 phase induction motor(without connecting supply) if we rotate its rotor by hand and check resistance of stator winding at motor terminal box its resistance varies why ??
1 hp single phase motor is more likely to get hot thsn inone hp 3 phase motor its true or false? If true why?
3 Answers Focus, Focus Energy,
if there are six generators (3 gas CATT, one Jenbacher o1 MW each, and two nos Diesel 01 no 01 mw other 0.65mw EDGs ( say), 3 CAtt gas set have identical pole pitch,01mw EDG and Jenbacher gas Set have different pole pitch, how their power connection can be done to connect a common bus bar during installation. in short, how different pole pitched generators power connection can be done to connect a common busbar system through generators incomer ACBs.
Unit of Magnetic Flux Density a) Tesla b) weber c) Hendry d) Farad
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)