in our 6.6kv motor feeder[it is having two sources from
Bus A&B] earth fault relay is acting, we checked CBCT
connection and cable meggerd values found very good still
earth fault acting during first two are three start after
that it will hold. please clarify what was the reason. if
same motor is starting from other Bus-A it will start.
WHAT IS THE TYPE OF 6.6KV SW.GR. hOW OLD IS THIS?
tHE EARTH FAULT RELAYS ARE VERY SENSITIVE. INSULATION
RESISTANCE OR MEGGER CAN NOT MEASURE.
CARRY OUT HV CAPACITANCE MEASUREMENT OF MOTOR,CABLE FEEDER.
AND hIGH POT TEST.
MEASURE THE TANGENT DELTA FROM DC HIGH POT.
IF MIN OIL CIRCUIT BREAKER,TEST THE OIL AND REPLACE.
WE ALSO EXPERIENCED THIS DUE TO BURNED CEREMIC/BAKELITE
PARTITION PLATES OF 6.6KV SW.GR
Is This Answer Correct ? | 0 Yes | 1 No |
What is the approximate value of stacking factor?
What is the general system requirement of alternator?
1> what r different types of fault in cables? How will u locate and test these faults? 2> why earth wire is provided on top throughout the transmission line. why not only on towers? How much area it can protect? 3> what r different types of transmission losses? How power loss can be minimized? 4> what is the % of power loss on transmission lines?
what is general test conduted by transformer
what is difference between megger & Contact resistance meter & its Application?
I need the proper answer on :- What is the Earthing Value as per the standard for Raw power and UPS Pit and in panel /DB N-E value ???
I Want randstand placement papers
How they LT panel busbar size choose
What is Diff btw MCP & MCB????
10 Answers Athena, Emerson, Suzlon,
state the working of discharge lamp?
HOW MUCH KVA DG SET REQUIRED for charging 12v 4000 ah battery?
Explain mechanical rotational system?