How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?
Answers were Sorted based on User's Feedback
Answer / noori
Hi
there are two methodes of temp.tx calibration:
1 - if u have MV sourse u have to get ambiante temp.MV & the
temp. you select and using themocouple vr. MV chart to get
the corresponding MV for these two temps.and for the same
thermocouple type
you have to subtracte the MV for ambiant from the MV for
your temp.
then yiu can inject this new MV to the input of the Tx
you have to get two tempretures for the calibration one for
ZERO &the second for span
you have to do the above prcedure for both points
2 - if you have temperature calibrator the you have to use
the same type of thermocouple immering it directly in the
calibrator and set the first point for Zero & set the second
point for span adjustment
| Is This Answer Correct ? | 3 Yes | 1 No |
IF U USE MV INJECTOR FOR THERMOCOUPLE CALIBRATION.........
FIRST U SHOULD MEASURE THE ROOM TEMPERATURE AND TO COMPUTE EQUELENT THERMOCOUPLE VOLTAGE.......V REF....
IF U R INJECTING 100 DEG EQULENT MV U SHOUD DEDECT V REF MV FROM THAT ACTUL MV...AND APPLY ADJUST 100.......
IF U R USING TEMPERATURE CALIBRATOR NO NEED THIS ONE ...U CAN APPLY DIRECT......BECAUSE IT GIVES THE COMBENSATED OUTPUT
| Is This Answer Correct ? | 3 Yes | 3 No |
what is mapping in instrumentation and control engineering
Why do we use triad cable for RTD to Temp.transmitter connection? Why we don't use 3 core cable?
1 Answers Process Control Technologies,
How INtools is useful for routine Instrument maintenance?
i/p converter always for supply pessure from 3~15 psi only !! And from where this converter bleed the air.
Why some transmitter shows flow in MMWC and some in TPH?
Explain PID controller tuning & any one method used for it.
how do calibrate the valves.. with clear manual
what is absolute pressure and where use in process?
What is DCS and PLC scanning time?
I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION. THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME TIME IT IS STABLE. WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY. WHERE AS INDICATION FLUCTUATES. WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE FIELD IT INDICATION IS STABLE. WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE. PLEASE CLARIFY.
How can I zero check of wet leg type DP Tx ?
Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)