How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?
Answers were Sorted based on User's Feedback
Answer / noori
Hi
there are two methodes of temp.tx calibration:
1 - if u have MV sourse u have to get ambiante temp.MV & the
temp. you select and using themocouple vr. MV chart to get
the corresponding MV for these two temps.and for the same
thermocouple type
you have to subtracte the MV for ambiant from the MV for
your temp.
then yiu can inject this new MV to the input of the Tx
you have to get two tempretures for the calibration one for
ZERO &the second for span
you have to do the above prcedure for both points
2 - if you have temperature calibrator the you have to use
the same type of thermocouple immering it directly in the
calibrator and set the first point for Zero & set the second
point for span adjustment
Is This Answer Correct ? | 3 Yes | 1 No |
IF U USE MV INJECTOR FOR THERMOCOUPLE CALIBRATION.........
FIRST U SHOULD MEASURE THE ROOM TEMPERATURE AND TO COMPUTE EQUELENT THERMOCOUPLE VOLTAGE.......V REF....
IF U R INJECTING 100 DEG EQULENT MV U SHOUD DEDECT V REF MV FROM THAT ACTUL MV...AND APPLY ADJUST 100.......
IF U R USING TEMPERATURE CALIBRATOR NO NEED THIS ONE ...U CAN APPLY DIRECT......BECAUSE IT GIVES THE COMBENSATED OUTPUT
Is This Answer Correct ? | 3 Yes | 3 No |
what is intools software
Hello friends i need check lists of different instruments during the Erection and commissioning in thermal power plant.Please help me.My Mail id is naba02222@gmail.com/naba02222@rediffmail.com Thanks Nabakishore Biswal
In 16' pipeline one pcv is installed which is controlled by PT installed at inlet of PCV.If Flowrate in pipeline increases what will happen to pressure at the inlet of pcv.
what is the minimum power (P=VI)to produce a spark?
How the warning lamp of a charging-system is activated ?
what is seebeck effect?
basic connection and principle of axial shift sensor n differential sensors in tubine describes n draw......
what is loop?
I am having a Phoenix digital to modbus converter. The o/p of the same is connected to flow computer FB407. But the digital signals are updated only after one minute in the flow computer. what may be the cause of delay in communication? Flow computer is having a scanning period of less than 1 sec.
what is proportional & what is proportional band
why we set -10 volt in vibration sensor output,why not +10 volt
what is o2 analyzer and how it measured ,what is the role of this analyzer in cfbc boiler...