How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?
Answers were Sorted based on User's Feedback
Answer / noori
Hi
there are two methodes of temp.tx calibration:
1 - if u have MV sourse u have to get ambiante temp.MV & the
temp. you select and using themocouple vr. MV chart to get
the corresponding MV for these two temps.and for the same
thermocouple type
you have to subtracte the MV for ambiant from the MV for
your temp.
then yiu can inject this new MV to the input of the Tx
you have to get two tempretures for the calibration one for
ZERO &the second for span
you have to do the above prcedure for both points
2 - if you have temperature calibrator the you have to use
the same type of thermocouple immering it directly in the
calibrator and set the first point for Zero & set the second
point for span adjustment
| Is This Answer Correct ? | 3 Yes | 1 No |
IF U USE MV INJECTOR FOR THERMOCOUPLE CALIBRATION.........
FIRST U SHOULD MEASURE THE ROOM TEMPERATURE AND TO COMPUTE EQUELENT THERMOCOUPLE VOLTAGE.......V REF....
IF U R INJECTING 100 DEG EQULENT MV U SHOUD DEDECT V REF MV FROM THAT ACTUL MV...AND APPLY ADJUST 100.......
IF U R USING TEMPERATURE CALIBRATOR NO NEED THIS ONE ...U CAN APPLY DIRECT......BECAUSE IT GIVES THE COMBENSATED OUTPUT
| Is This Answer Correct ? | 3 Yes | 3 No |
Explain why plc require in analog input 4-20amp & 0-10 volt?
What is glanding
if my 6 kva UPS gives 20 min. backup at 100 % load, then at 25% load what is the backup time?
if temperature transmitter is showing wran. sensor 2 fail how can you remove from the transmitter display m/n.3144p rosemount
When cryogenic control valve will be applied?
During the design and engineering of a process plant, a good designer should plan for ____________, ___________ and ____________ aspects of the plant
where the use of direct action control valve?
SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS INITILAZIATION PLEASE HELP ME READRING THIS?
Why we are measuring 4-20ma? Why we are not taking 0-20ma? Plz answer this
When LP SURGE happening in compressor
Why we are using reverse action in displacer types level transmitters on some Vessels?
WHAT ARE THE INSTRUMENTAL DIAGRAMSOF VALVES?
0 Answers Artikal, ITC Infotech,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)