How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?
Answers were Sorted based on User's Feedback
Answer / noori
Hi
there are two methodes of temp.tx calibration:
1 - if u have MV sourse u have to get ambiante temp.MV & the
temp. you select and using themocouple vr. MV chart to get
the corresponding MV for these two temps.and for the same
thermocouple type
you have to subtracte the MV for ambiant from the MV for
your temp.
then yiu can inject this new MV to the input of the Tx
you have to get two tempretures for the calibration one for
ZERO &the second for span
you have to do the above prcedure for both points
2 - if you have temperature calibrator the you have to use
the same type of thermocouple immering it directly in the
calibrator and set the first point for Zero & set the second
point for span adjustment
| Is This Answer Correct ? | 3 Yes | 1 No |
IF U USE MV INJECTOR FOR THERMOCOUPLE CALIBRATION.........
FIRST U SHOULD MEASURE THE ROOM TEMPERATURE AND TO COMPUTE EQUELENT THERMOCOUPLE VOLTAGE.......V REF....
IF U R INJECTING 100 DEG EQULENT MV U SHOUD DEDECT V REF MV FROM THAT ACTUL MV...AND APPLY ADJUST 100.......
IF U R USING TEMPERATURE CALIBRATOR NO NEED THIS ONE ...U CAN APPLY DIRECT......BECAUSE IT GIVES THE COMBENSATED OUTPUT
| Is This Answer Correct ? | 3 Yes | 3 No |
Why DP level transmitter preferred for closed vessels and Radar level transmitter for open tanks??
INtools Trainining
1 Answers Monarch Techno Engineering Solutions,
How is PH sensor works ?
i m passed my engineering in 2010 in instrumentation and control engineering. my question is can i apply for software jobs or vacancies.??????????? plz give me answer soonnn......
what is the pressure in the tank when its level of liquid is 1.5 meters when its total capacity is 2 meters
Why 4-20mA SIGNAL IS PREFERRED OVEA A 0-10v signal?
what is Automation?
How to convert mmWc(mili meter water colam) to tph(ton per hour)?
In vortex flow meter how can measure the frequency of vortex generated by vortex flow meter
Condensation within a sight glass? Would you expect there to be more problems when using a sight glass if there is condensation on the inside or the outside of the glass, and why?
What is the role of P(Protional), I(Integral) and D (Derivative) in PID Controller?
what is difference between call out and call log
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)