Why some transmitter shows flow in MMWC and some in TPH?
Answers were Sorted based on User's Feedback
Answer / anwar azim
Flow is propotional to sqare root of DP across the flow
element.Since this difference is very small the transmitter
is calibrated in the range mmWC.When the display is
according to range i.e 4-20mA FOR 0-2500MMwc tx shows flow
in mmWC.When one converts the range into engineering values
i.e 0-30TPH corresponding to 0-2500mmWC ,the tx show the
flow in TPH.The same can also be seen in percentage also.
| Is This Answer Correct ? | 25 Yes | 3 No |
Answer / ashish namdev
MMWC is a unit of differential pressure but TPH is a unit of flow rate.MMWC can be convert in flow rate
Q = ^P
| Is This Answer Correct ? | 7 Yes | 0 No |
1.what is beta in control valves? 2.what is the condition followed by light in LASERs? 3.1kg/cm2=?psi 4.Integral action reduces what? 5.about vena contracta 6.a simple RC circuit 7.thermistor material's temp coefficient of resistance 8.if wave passes through the thicker area of a chord to a thinner area what changes will occur to wavelength? 9.if 4-20 mA represents 0-10 kg/cm2 what will be the current when pressure is 5 kg/cm2.................
when the operation engineer told you that he gives the control valve order to open but there is no response ! what will you do ? and if you found that there is astuck , what will you do ? (note : it is apanumatic valve )
what is sliding spool valves?
what should be distance from tapping point to inallation place of instruments?
3 Answers Tasnee Petrochemicals,
Guy's need your support,I want to measure closed tank level which is under vacuum -630mmHg using DP Transmitter, tank fluid density 1.38, Tank height is 7ft
I want to use 1/2 inch SS316 tube in my high pressure & temperature (64 kg/cm2 & 500 deg C)after condensate pot in pressure tranmistter. 1) Is it possible to use 1/2" ss316 tube in high pressure and temperature line. Tube manufacturer is local vendor. 2)On sarting the plant, We need to do system fluse that time condesate is not in the condesate pot so steam is directly contact with the tube. We have no exact calculation to know our tube is ok or nor at this time. pleae,reply.
what is the differnce betweeen hart and smart tx
Why 4mA-20mA current loop selected as standard ???
difference b/w single acting and double acting actuator by using application only?
what is o2 analyzer and how it measured ,what is the role of this analyzer in cfbc boiler...
What is PLC(programmable logic control)?
what should be the attitude while answering an interviewer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)