Why some transmitter shows flow in MMWC and some in TPH?
Answers were Sorted based on User's Feedback
Answer / anwar azim
Flow is propotional to sqare root of DP across the flow
element.Since this difference is very small the transmitter
is calibrated in the range mmWC.When the display is
according to range i.e 4-20mA FOR 0-2500MMwc tx shows flow
in mmWC.When one converts the range into engineering values
i.e 0-30TPH corresponding to 0-2500mmWC ,the tx show the
flow in TPH.The same can also be seen in percentage also.
Is This Answer Correct ? | 25 Yes | 3 No |
Answer / ashish namdev
MMWC is a unit of differential pressure but TPH is a unit of flow rate.MMWC can be convert in flow rate
Q = ^P
Is This Answer Correct ? | 7 Yes | 0 No |
How to calibrate DP tramitter in flow measurement application? consider my range of flow is 0 to 2000 kg/hr ? please give calculation of , How much pressure applied on low pressure side and high pressure side please give detail of calculation .... It so important for me please reply as soon as possible
What is rated capacity in Control valve
What is close loop ?
1 Answers College School Exams Tests, GMR,
what are the inputs (drawings) we need to prepare loop schematics??
How to calibration coriolis flow meter?
what is instrumentation?
Can anybody explain what is the different between ESD & PLC
What is fault tolerent system
What are the characteristics of Control Valve
why use 50% lel methane gas concentration for gas detector calibration instead of 60% lel gas concentration whereas the hi alarm set at 60% lel.
what is Potential free contact? where it is used?
3 Answers Engineers India Limited,
Is it ok, to use non-contact type Radar type LT, on a tank that is half circular from the bottom side? If yes the, isn't the waves gonna bent in other directions?
0 Answers Process Control Technologies,