I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION.
THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO
A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME
TIME IT IS STABLE.
WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY.
WHERE AS INDICATION FLUCTUATES.
WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE
FIELD IT INDICATION IS STABLE.
WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE.
PLEASE CLARIFY.
Answers were Sorted based on User's Feedback
I agree with Mr. Satyendra Bhai Patel suggestions.
More over please check followings:
1. May be some electric motor starts and its cable routing
is near to your extension cable.
2. Also get check thermocouple,some time,its hot juction
got open and close with the passage of time. Replace
thermocouple.
3. Check loose connections.
4. Check thermocouple any wire being grounded at some time.
5. Any how, do not megger thermocouple extension wire.
Check it with normal multimeter.
aftabmazari@yahoo.com
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / satyendra bhai patel
check cable is screened or not ? i think this type of
problem occures when a little bit induction in wire .so
just screen your cable in indicator s terminal.problem will
be solved .
For more details u can contact me on 9005091827
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rana mujahid
I agree with all above answers but I think the most chances
are may be TC hot junction is some time going to open and
close..........need to replace TC
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / abhishek
please check instrument cables are earthen or not with
screened cables.this things only happens when wires are cut
at gland side or terminations are loosed
Is This Answer Correct ? | 0 Yes | 1 No |
what is diff between the motor and pump
I am an intru engg frm pune n completing mba marketing in may 2010, what kind of profile would best suit my educational qualifications??? Also, i will move to US in jan 2011, so this job experience should count Over there too 'coz i want to continue workin even there....
what do you know about Foundation Fieldbus?
What is i/e or o/p transmitter(ma/v)?
Why only negative 24 vdc supply give in vibration measuring system.
field bus transmitter calibration procedure tell me
compare the thermocouple and pyrometer,which one is the best?why?
INtools Trainining
1 Answers Monarch Techno Engineering Solutions,
What is principle of ultrasonic level transmitter?
What is the live zero and dead zero
what is the imbustion control loop
how to calibrate absolute pressure transmitter