I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION.
THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO
A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME
TIME IT IS STABLE.
WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY.
WHERE AS INDICATION FLUCTUATES.
WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE
FIELD IT INDICATION IS STABLE.
WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE.
PLEASE CLARIFY.
Answers were Sorted based on User's Feedback
I agree with Mr. Satyendra Bhai Patel suggestions.
More over please check followings:
1. May be some electric motor starts and its cable routing
is near to your extension cable.
2. Also get check thermocouple,some time,its hot juction
got open and close with the passage of time. Replace
thermocouple.
3. Check loose connections.
4. Check thermocouple any wire being grounded at some time.
5. Any how, do not megger thermocouple extension wire.
Check it with normal multimeter.
aftabmazari@yahoo.com
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / satyendra bhai patel
check cable is screened or not ? i think this type of
problem occures when a little bit induction in wire .so
just screen your cable in indicator s terminal.problem will
be solved .
For more details u can contact me on 9005091827
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rana mujahid
I agree with all above answers but I think the most chances
are may be TC hot junction is some time going to open and
close..........need to replace TC
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / abhishek
please check instrument cables are earthen or not with
screened cables.this things only happens when wires are cut
at gland side or terminations are loosed
Is This Answer Correct ? | 0 Yes | 1 No |
sir i m preparing for BARC but i am not getting any papers to prepare for this exam so please send me some sample papers to my i.d for the preparation of barc.
What is offset in a control system.
what r all the closed loop used in boiler? for this related tell some web address..
what is difference between venturi and orifice
Can we get the outpot in c without using getch fiction? Answer is yes but output will stay on display 4 only few second.... But can we get output without using getch and also output will hold on the display...?
full process of gas turbin?
i/p converter always for supply pessure from 3~15 psi only !! And from where this converter bleed the air.
Is there any temperature compenasation for the air flow from FD fan & SA fans which supplies air to the Boiler?
hello i'am samad.Any one Can help me! How to calibrate Vaccum Transmitter DP Type range 0 - 50 mbar abs by hand pump calibrator.
can u please tell me the different types of valve uses and wt purposes it is used ~!(controlling the flow other than that which valve should be used in what place)
Please send the all question with answer related for interview.
In your own words, would you expect an ultrasonic level device to work better in a pressure vessel with a high pressure or a strong vacuum, and why?