how to can we synchronize different capacity of DG
sets.60kva& 250kva?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Synchronization is as usual.The load sharing depends upon
fuel feed to prime movers
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / kj
As per the previous answer, synchronising is not a problem.
Using a load sharing module which is set up correctly will
allow the sets to share the load on a percentage basis. In
other words if the load is say 200 kva the load would be
about 65% on each or 38 kva and 161 kva.
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the string efficiency
What will happen if the rotor circuit of a slipring I.M. is kept open & electric supply is given to its stator winding.
Ceiling fan motor wiring Hi, I have 2 ceiling fans broken. The receiver/control units burned out due to lightening. One Harbor Breeze and one Hunter's I took them apart (remove receiver units). Now on both of the motor I see 4 wires coming out from each motor I really want to know the function of each wire. Are there anyway I can test to see which is which? After searching forums I know these 4 wires are from 2 sets of coils inside the motor, one is Start winding and the other is Runing winding I could not find the receiver/control unit any where, so I am planing to buy Capacitors and universal remote controls to make the fans run again. Anyone has any idea how to do the wiring, please help Thnks
IF we have 500kva transformer 11.0/0.415V, 50Hz. How to calculate the current on HT & LT side, how can we consider for its breaker (HT & LT both)? You are requested to solve the question herewith.
3 Answers Bhutan Power Corporation,
Draw an S.L.D of the main panel for a hospital, showing meter position. Essential loads are: 1) Equipment load 100 KW 2) Critical load 500 KW 3) Life AID Safety load 400 KW 4) NON-Essential load 200 KW 5) Other service loads 200 KW Calculate and suggest the size of the transformer, size of main cable, capacitor bank, and calculate the capacity of an emergency load having above first three mentioned loads is supplied by an emergency generator.
What is effect on in zone and out zone fault if CT chosen for phase side is Vk/2<5mA and Neutral side is Vk/2<15mA on REF protection of Transformer
What do you mean by per capita requirement of electrical energy in india
Sir, plz tell me how droop setting is done in parellel operation od DG set ? please give practical example ?
What is working principal of V.C.B., O.C.B., A.C.B & Over load relay?
what is an unbalance in acircuit? in a three phase 3wire circuit how an unbalance will come? in a three phase four wire system how an un balance is coming?
What is the diff. between single compression and double compression gland
How can I model an open-delta ground transformer for a network supplied by 4 unit GTG and power transformer in ETAP?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)