how to calculate the input current in singel phase and
3phase supply to 5kva ups
Answer / h s dhillon
Let the supply is 3 ph 4 w having line voltage 400 volts
and phase voltage 230 volts,then:
in case of single phase:
I=5000/230=21.74 Amp
In case of 3 phase:
I=5000/Under root3 i.e.1.732x400
=7.22 Amp
Is This Answer Correct ? | 7 Yes | 2 No |
what will happen if i will done heart shape hole in transformer core?
induction motor. we have a three phase supply from diffrent source like R= transformer. Y = DG sets. B = ups. if motor is runing.
The earth pin of some three pin plugs are seen split. why?
How can we get d.c series motor characteristics by using a.c induction motor?
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
which generator is called as brushless excitation generator and why??
Explain Creepage Distance of Insulator
What is Hi-Pot Test for Grid Station HV Equipments?
mccb service sittings be done?
How to protect a Dosing pumps/any sensitive equipment (single phase) from surge protection inside a food factory.
i purchase a microwave which is 50/60Hz but Current Setting 60Hz in my country we usually use 50hz, can i use AVR to solve my problem?
What is principal to reduce earth leakage current with isolation transformer? When isolation transformer is installed in input stage of system, earth leakage current is reduced. the reason is why the leakage current of 2nd stage of isolation transformer does not affect the 1st stage's leakage current. I would like to know the reason. As you know, earth leakage current is a kind of AC. So, How to reduce earth leakage current in case that isolation transformer is used?