how to calculate the input current in singel phase and
3phase supply to 5kva ups
Answer / h s dhillon
Let the supply is 3 ph 4 w having line voltage 400 volts
and phase voltage 230 volts,then:
in case of single phase:
I=5000/230=21.74 Amp
In case of 3 phase:
I=5000/Under root3 i.e.1.732x400
=7.22 Amp
| Is This Answer Correct ? | 7 Yes | 2 No |
What is resolver and glass scale in CNC how they work?
what are the effects of variations in frequency when you are connected to national grid??
Caliculate the Specific Fuel consumption of 320 kva diesel genarator set?
why we are used thermistor in motor
Why VCB and SF6 breakers to be used in HT used by cant ACB of higher rating to be used for 11kv and 33kv.
WHAT ARE THE CHARACTERISTICS OF AN VOLTAG AMPLIFIER
Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.
What is the principle of Excitation.
how many parameters can integrate with fire alarm basically ?
2 hp motar how many amps taken please show me the formula
What is the formula for calculating the Instantaneous Short Circuit & overcurrent for any breaker
How much CTs are required to measure th curent in DOL starting of motor?PLs explain.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)