what is air to open and air to close control valve and
difference btwn this...and how to measure milli amp by
this...and what is the role of positioner and i/p converter in
this..plz help me
Answers were Sorted based on User's Feedback
Answer / anwar mydeen
Air to open valve: the pneumatic valve will open when the
air is applied in to the actuator chamber. and the valve
will goes to close condition when u remove the pneumatic air.
In oil industry oil outlet and produced water outlet control
valves are air to open valves.
Air to Close: the pneumatic valve will close when the air is
applied in to the actuator chamber and the valve will goes
to open condition when u remove the pneumatic air.
| Is This Answer Correct ? | 63 Yes | 5 No |
Answer / mohammed abdul rahman
This query is mostly related to pneumatic diaphragm actuated control valves. Air to open valves have the pneumatic input on the under-side of the diaphragm with a spring on the topside, which causes the valve to open on increase in control signal. Air to close valves will have the pneumatic input on the topside of the diaphragm with a spring on the under-side to provide counter force.
An i/p converter will convert the 4-20mA signal from control system to an equivalent 3-15psi pneumatic signal to actuate the control valve.
A positioner will have the i/p converter inbuilt and is connected to the moving part of the valve and automatically adjusts the signal to the actuator to maintain a position proportional to the signal. This introduces a loop inside a loop.
Please refer the control valve handbook from Fisher for reference. It is available as a free download.
| Is This Answer Correct ? | 37 Yes | 4 No |
Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system
Why 4mA-20mA current loop selected as standard ???
In the field and in the control room different power supplies if used How to handle the ground
when the operation engineer told you that he gives the control valve order to open but there is no response ! what will you do ? and if you found that there is astuck , what will you do ? (note : it is apanumatic valve )
what is the procedure to isolate flow a transmitter and flushing it?
what is the diffrence between mmwc and kg/cm2 for pressure measurment when we are using mmwc and when kg/cm2 and why????? ?? what is the reason
19 Answers Ecoboard, Jindal, Sepco,
what is temperature compensation?
I wnat to practice more online type questions .so will you show them me to take a practice test?
in a power plant main steam flow is volumetric or mass flow? is it required compensation?
what is flow equation of kg/hr to m3/hr
What is the diffrence between digital signal processing and discrete signal processing?
why does a transmitter o/o signal starts from 3-15psi or 4- 20mA?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)